Lighting Circuit.. Surely This Isn’t Right? | Page 2 | on ElectriciansForums

Discuss Lighting Circuit.. Surely This Isn’t Right? in the Lighting Forum area at ElectriciansForums.net

Its the same question as a year ago but there was no answer
50w at 230v i=p/v i=50/230 i=0.28 amps
50w at 12v i=50/12 i=4.2 amps
Is this correct?
 
You are forgetting that you are working it out at 12 volts, if you transpose it to 240 volts (for ease of calculation then divide your 4.2 amps by 20 which comes to 0.21 amp, so 5 LV lights to 1 ampish, so why not put 20 or so lights on a circuit, calcs work out alright.
 
Don't forget to add in the power factor load of the transformers ;)

On a serious note, all these quotations of loads on the 1.0 don't mention that the cable should be de-rated as, being a lighting cable, it will undoubtedly be going through loft insulation, bunched with other cables, and goodness knows what else on its route, knocking the CCC down considerably. I know 'official' cable calcs often give ridiculously pessimistic results, like demanding a 10mm cable for a lighting circuit because of all the factors, but in this case 1.0 really doesn't seem enough.

It would be be interesting to do a proper calc with the given load, and all the insulation, grouping, and other factors, and real length and see what it comes up with.
 
and did any one mention diversity..... ive pushed circuits to limits .... forget future proofing...... will keep us in work and are quotes will be slightly cheaper
 
You can probably count the amount of times ALL of a circuits lights are on, within a domestic setting on one hand over the lifetime of the installation!! As far as i'm aware, 100W incandescent lamps are no longer available, and 60W lamps are soon to follow.

I'm not saying that the circuit as described by the OP is a particularly good one, but most are over assessing the actual demand load that this circuit will ever see!! Diversity is a wonderful thing, to those that know how to use it!!! lol!!
 
Oops didn't read the date! It was on the front page so I thought it was quite recent. Never mind, that house has probably burnt down by now, from a 1.0 cable melting onto some newspaper in the loft!
 
Yes it is. I've never liked the idea of diversity on lights. In houses inhabited by rich and/or lazy people it is common to have all lights blazing all day and most of the night whether anyone's in the house or not. In my two-room hovel it is very common to have both candles alight at once, so no diversity here...
 
haha!! Are you saying that it's common for householders to have every lamp switched on a circuit, including exterior lighting?? I don't know what world your living in but it's not mine. Diversity ''always'' needs to be applied, especially in domestic installations, or you'll be asking the DNO for a cut out fuse of around 160+A.
 
haha!! Are you saying that it's common for householders to have every lamp switched on a circuit, including exterior lighting?? I don't know what world your living in but it's not mine. Diversity ''always'' needs to be applied, especially in domestic installations, or you'll be asking the DNO for a cut out fuse of around 160+A.

not in my house, kids leave bathroom lights on , bedroom lights on, living room lights on.
my kids don't do diversity...........:coolgleamA:
 
not in my house, kids leave bathroom lights on , bedroom lights on, living room lights on.
my kids don't do diversity...........:coolgleamA:

Well that would be across 2 circuits from your description here, up and down stairs circuits. .lol.!! If you let your kids go round switching every light switch on in the house, and leaving them on, then more fool you.

In domestic surroundings, it's unlikely that the lighting circuits will be drawing a fraction of the cables or protection devices rating!!
 

Reply to Lighting Circuit.. Surely This Isn’t Right? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I will do this at the next visit and zs at the furthest point
Replies
10
Views
1K
To be honest Markelect, You have had a good 25 years trouble free, I wouldn't waste any more time and effort and just go for a full replacement on...
Replies
10
Views
2K
Thanks little spark. Good point but the drivers I'm considering have a sync and communication between driver function. So (as long as it works)...
Replies
6
Views
481
Hello What was the conclusion of your problem?
Replies
1
Views
721
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks