Hi

There is a lighting circuit fault in a property with the downstairs lighting circuit. I have tested the voltage and there is 230v on both line and neutral conductors going to the light pendnat although the pendant (any pendant) isnt showing light . no changes have been made to the lighting . there is a pendant in the hall and there is downlights around 12 in total and i have checked the junction boxes for the downlights and there is no loose connections
??

thanks
 
What are you measuring this voltage with?
You are probably best doing continuity tests.
 
  • Like
Reactions: DPG
What are you measuring this voltage with?
You are probably best doing continuity tests.
using a multifunction tester testing between earth and line and earth and neutral on the ceiling rose
 
You shouldn't have 230v between earth and neutral. Check polarity. If polarity is right, neutral has a break in it somewhere.
i removed the switch line also and then the pendant was still live
 
You need to do continuity tests.
As above you shouldn't have 230v between neutral/earth, are you getting this?
 
  • Agree
Reactions: James
What about between L and N? Did you measure that voltage?
yes its 230v i am going back there today to get access to the final junction box for the other downlights to see if there is any loose connections. its the strangest fault ive seen
 
Measuring voltage is not going to verify to effectiveness of conductors. Have you tried doing an earth fault loop impedance test across line and neutral.
 
Measuring voltage is not going to verify to effectiveness of conductors. Have you tried doing an earth fault loop impedance test across line and neutral.
I will do this at the next visit and zs at the furthest point
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Light circuit fault. 230v on l and n no light working
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
sid521,
Last reply from
sid521,
Replies
10
Views
1,575

Advert