what should the main earth bond size cable be.? Which part of regs will point me in right direction?
Thanks
 
Sorry do appologise just read my post.. I can get my main earth size from adiabatic table.. My question was for main equapotential bond to water incomer.?
 
Edit...

BS7671. 544 Protective bonding conductors.
 
Last edited by a moderator:
Vital info missing see post 5.

Although your 3ph 4core comment suggests TNS or is this misleading us?
 
Its a tn-cs.. Thanks for your info.!
 
544. says with tail size greater than 150mm maximum equipitential earth size is 50mm and s/2 for your main earth bonding there only need 95 120 is over sized
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

bigspark17

Arms
~
Joined
Location
wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Main earth bond commercial..
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
bigspark17,
Last reply from
jonney88,
Replies
7
Views
1,844

Advert