Can i wire led ceiling lights, 1 x extractor fan with fused isolation switch and a double socket from a 13a fused spur
 
You can, but the lights and the fan will need another fuse, to limit the current to 5or6 amps.
 
Typically you would use a FCU (fused connection unit) for fusing down the supply for lights in such a scenario, as most light switches are rated at 10A and some lights specify a maximum over-current protection value for safety.

The lights are unlikely to need more than an amp or so anyway, so it may well be practical to use a 3A FCU for supplying both the lights and fan, with the fan simply on an isolation switch.
 
  • Like
Reactions: DPG
Is the socket outlet part of the ring final circuit, is the socket already spurred from the ring final circuit or is the socket part of a radial circuit.
 
Typically you would use a FCU (fused connection unit) for fusing down the supply for lights in such a scenario, as most light switches are rated at 10A and some lights specify a maximum over-current protection value for safety.

The lights are unlikely to need more than an amp or so anyway, so it may well be practical to use a 3A FCU for supplying both the lights and fan, with the fan simply on an isolation switch.

Is the socket outlet part of the ring final circuit, is the socket already spurred from the ring final circuit or is the socket part of a radial circuit.
Just to confirm the layout is correct.
Spur taken from double socket off final curcuit. To a 30a fused wall box then to 1x double socket to 5amp fused box 3 core + earth to led light then on to extractor. from light to switch and thanks much appreciated
 
30A fused wall box?
 
  • Like
Reactions: DPG

I don't wish to sound uncharitable, but I don't believe that for one second and suspect those numbers have been lifted from post #2, after you originally asked if it was okay to run the fan and lighting from a 13A fused spur.

Ensure the fan is installed in accordance with the manufacturer's instructions, regardless of who installs it, as failure to observe those instructions could result in fairly dire consequences.


**I'm not an electrician, but simply someone concerned by what you've posted**
 
  • Like
Reactions: Dartlec
I don't wish to sound uncharitable, but I don't believe that for one second and suspect those numbers have been lifted from post #2, after you originally asked if it was okay to run the fan and lighting from a 13A fused spur.

Ensure the fan is installed in accordance with the manufacturer's instructions, regardless of who installs it, as failure to observe those instructions could result in fairly dire consequences.


**I'm not an electrician, but simply someone concerned by what you've posted**
Ok thats cool
 
Does the fan manufacturer specify a 5A fused supply?

Seems unusual.
I fitted a fan not that long - I think it may have been an Xpelair - that did specify a 5A fuse in the MI, which is unusual as they often seem to state 3A.
 
  • Like
Reactions: nicebutdim
Just to confirm the layout is correct.
Spur taken from double socket off final curcuit. To a 30a fused wall box then to 1x double socket to 5amp fused box 3 core + earth to led light then on to extractor. from light to switch and thanks much appreciated
Assuming the existing socket circuit is a Ring Final Circuit (on a 32A breaker), then unfortunately that is a spur off a spur which isn't compliant -

If the final circuit is a 20A or 16A radial then it would be compliant, but on a Ring Final Circuit you'd have to:

Ensure you are taking a feed from a socket on the ring
Fit a 13A Fused spur before the socket -
Feed the socket and the 5a Fused spur from that.

And ensure that RCD protection is in place as it is new wiring
Plus ensure you have complied with part P notification requirements if work in a bathroom is involved.

A lot is involved in what can seem simple extension work to ensure it is done safely and legally.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New bedroom wiring
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Karlb1,
Last reply from
Karlb1,
Replies
15
Views
1,872

Advert