R2 test on a ring main where the conduit is the earth

Discuss R2 test on a ring main where the conduit is the earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A wander lead is the correct method of testing conduit containment systems, though far better using a high current ductor tester!! All conduit system fed accessories should have a flying lead from box to face plate. Don't know why anyone would think you can't carry out ELI tests on conduit systems without a separate CPC?? You just don't, or shouldn't need them!!
 
it's a bit like earth bond testing when doing PAT. high current, but a more accurate resistance measurement. the high current will show up any corroded joints in the conduit.
 
Ive never come across or wired a conduit system using it as the earth. Always been in the spec that separate cpc needed. What is a high current doctor thingy then 54?

Shouldn't really be calling it a Ductor tester really, as Tony Say's a true ductor tester is generally a high current milli/micro ohm tester!! It's basically a high current ohm meter that tests the bonding/continuity of conduit/trunking containment systems on a wander lead basis. Most used to know these bit's of kit as the ''Clare Tester'' The early ones used to come in an integral wooden case...

Never seen a professionally produced electrical specification that calls for a separate CPC to be pulled into a metallic containment system, as it's a costly and totally pointless exercise!!!
 
well so far I have done two schools, a college, a hospital and a fire station in steel trunking and conduit and have pulled in same size pvc single cpc in every one. Labour only so I'm not worried about the cost lol.
 
I'll just point out again, a totally pointless and costly exercise!!

Thankfully, i've never seen such a specification in all the years i've been in the industry!!
 
Most used to know these bit's of kit as the ''Clare Tester'' The early ones used to come in an integral wooden case...

Woe betide you if you forgot to put it on charge at the end of the day!
God help you if Jim the tester’s mate found you’d got dirt on the polished wooden case! The ones we had wouldn’t have looked out of place on mother’s sideboard.
 
Woe betide you if you forgot to put it on charge at the end of the day!
God help you if Jim the tester’s mate found you’d got dirt on the polished wooden case! The ones we had wouldn’t have looked out of place on mother’s sideboard.

Many of these conduit testers were mains powered units, in fact i can't say that i've used a battery unit myself... lol!! But your right about those older wooden boxed units, works of art they were!!...lol!!
 

Reply to R2 test on a ring main where the conduit is the earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock