Hello, I've found an old motor originally designed for operating jealousies.
Could you help me read and better understand the following schematic?
As far as I understand, it is a single phase induction motor, there is 47 uF capacitor connected to it in order to start.
There are 3 contacts marked 1, 2, 3 + PE. There is also a switch button.
What would be the correct way to wire 1, 2, 3 contacts? What is the purpose of the switch button? (change of rotation direction?)
I measured resistance between these:
12 - 121.7 ohm
23 - 242 ohhm (both windings?)
13 - 120.5 ohm

Thank you

20190914_180406.jpg
 
The motor is a permanent split capacitor type (it is not a starting capacitor, it is in circuit all the time the motor is running, and is probably 4.5μF not 45.)

The circuit for these is standard. Ignoring the limit switches etc and concentrating only on the motor, the neutral connection goes to the junction between the windings, terminal 6, the capacitor connects between the two other ends as shown (at terminals 4 & 5). Connecting line to terminal 4 will run the motor one way, terminal 5 will run it the other way. You will note that in each case, one winding is energised directly from the supply, the other via the capacitor. The direction of rotation depends on which winding receives a leading phase shift by being connected to the capacitor.

If you can only get to terminals 1,2,3 and not 4,5,6, you can connect neutral to terminal 1, line to 2 or 3 for forwards or reverse. However there will be a limit switch connected in one direction, the manual switch in the other, and what looks like a thermal cutout overall. If it is indeed a thermal cutout, you should make the neutral connection to terminal 1 (not 6) anyway.

Note that the motor is short-time rated only (KB= Kurzbelastung) 4 minutes maximum followed by a cooling period typically of 15 mins. This is on account of the compact size of the motor not having enough surface area to dissipate the heat produced.
 
Last edited:
The motor is a permanent split capacitor type (it is not a starting capacitor, it is in circuit all the time the motor is running, and is probably 4.5μF not 45.)

The circuit for these is standard. Ignoring the limit switches etc and concentrating only on the motor, the neutral connection goes to the junction between the windings, terminal 6, the capacitor connects between the two other ends as shown (at terminals 4 & 5). Connecting line to terminal 4 will run the motor one way, terminal 5 will run it the other way. You will note that in each case, one winding is energised directly from the supply, the other via the capacitor. The direction of rotation depends on which winding receives a leading phase shift by being connected to the capacitor.

If you can only get to terminals 1,2,3 and not 4,5,6, you can connect neutral to terminal 1, line to 2 or 3 for forwards or reverse. However there will be a limit switch connected in one direction, the manual switch in the other, and what looks like a thermal cutout overall. If it is indeed a thermal cutout, you should make the neutral connection to terminal 1 (not 6) anyway.

Note that the motor is short-time rated only (KB= Kurzbelastung) 4 minutes maximum followed by a cooling period typically of 15 mins. This is on account of the compact size of the motor not having enough surface area to dissipate the heat produced.
Thank you for explaining the principal and clarification. It works exactly the way you described. You helped me a lot, have a good day!
 

Reply to Single phase induction motor schematic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Forum Members I have a 4 pole single phase 240VAC 315 watt motor from a central heating heating system that I think is bad. It's the room fan...
Replies
18
Views
2K
hello!! hope anybody can help me. I have an AC single phase 220v 1.5HP motor that won't rotate when plugged in even when I try to do it by hand...
Replies
5
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock