Just wondering if I got this right but is it ok to take a 2.5mm spur from a 32MCB ring main Or should I use 4mm cable.
 
Have a look at Appendix 15 of the BBB (Page 505)
 
You can spur 1 double or 1 single on 2.5mm
 
  • Like
Reactions: Ashley-Joseph
  • Like
Reactions: Spoon and DPG
Yeah my other thoughts were to just ad a 20MCB with a 2.5mm radial for 1 socket.
 
Yeah my other thoughts were to just ad a 20MCB with a 2.5mm radial for 1 socket.
Appendix 15 should ex[plain it all, a good read is required.
 
  • Like
Reactions: Ashley-Joseph
The 2.5mm the spur is made with has an advantage ,
it is not evolved in the current flowing thru the rest of the ring .
(that may already be well loaded)
 
  • Like
Reactions: Ashley-Joseph
The 2.5mm the spur is made with has an advantage ,
it is not evolved in the current flowing thru the rest of the ring .
(that may already be well loaded)
Sorry, explain please
 
Sorry, explain please
(Tin hat in place)
a) Attempting to explain where common sense seems to imply --with 2x 2.5 entering a socket in RFC ,that 4mm might be more appropriate for spur wiring...
(ignoring physical constraints of the situation)
b)(or is the situation confused with spur/radial references .. -5 Skill points)
 
I think 4mm is more suited as Iz has to be higher than In.
 
Yeah my other thoughts were to just ad a 20MCB with a 2.5mm radial for 1 socket.
You could, but that is a new circuit with the need to notify the work to the local authority. Not worth the PITA.
 
I see plenty of EICRs stating that 'multiple circuits' are connected into 1 breaker and need rectifying. On inspection it's often just a spur taken from ring at MCB and no issue at all!
This is a common misconception, 'multiple circuits' in one MCB is an impossibility by definition. If there is one point of connection to a protective device at the source of supply it is one circuit no matter how many cables are connected.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Milton Keynes
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Spur from 32MCB
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
Ashley-Joseph,
Last reply from
j1mbodrea,
Replies
17
Views
2,689

Advert