The 2.5mm the spur is made with has an advantage ,
it is not evolved in the current flowing thru the rest of the ring .
(that may already be well loaded)
 
Sorry, explain please
(Tin hat in place)
a) Attempting to explain where common sense seems to imply --with 2x 2.5 entering a socket in RFC ,that 4mm might be more appropriate for spur wiring...
(ignoring physical constraints of the situation)
b)(or is the situation confused with spur/radial references .. -5 Skill points)
 
I think 4mm is more suited as Iz has to be higher than In.
Your spur will not require overload protection as long as the load can not exceed the Iz of the spur cable so at most you can only have a max load of 26 amps from one double socket which is highly unlikely that that is what will be used.
2.5mm is more than adequate for a single spur
 
If you look at appendix 15 you will see that you can spur from the origin in 2.5 which will negate the need for a 20A mcb as you suggested in your post 7
 
I see plenty of EICRs stating that 'multiple circuits' are connected into 1 breaker and need rectifying. On inspection it's often just a spur taken from ring at MCB and no issue at all!
This is a common misconception, 'multiple circuits' in one MCB is an impossibility by definition. If there is one point of connection to a protective device at the source of supply it is one circuit no matter how many cables are connected.
 

Reply to Spur from 32MCB in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock