I'd appreciate some second opinions here, as I've been sat here assessing the various symptoms of a situation, and coming to the conclusion that it seems to add up to a either a lost neutral, or high resistance neutral situation, and trying to work out if I need to be giving the building owner a ring over the weekend...
Situation is a factory unit, 3 phase, TN-C-S, 100amp per phase supply, at the end of a fairly long supply line at the extremes of it's capacity, and I think with several other units being fed from the same line prior to the factory, the DNO installations is probably 50+ years old.
Symptoms are
1 - extreme imbalance of the phase voltages, with the phases eg 250, 238, 220V respectively during the day when the 3 phase printing machines were operating relatively well balanced load, then just as I was being ushered out of the door with all the machines off and only a small single phase load for office lights, fridge, etc, I went to check why our inverter wasn't working and the voltage readings were showing something like 280, 250 and 180V respectively.
2 - Getting a few minor shocks between neutral and the earthed metal trunking on a little sub board with the 3 pole breaker feeding that board switched off.
We'd fitted a 30kWp solar PV system a month or so ago, but this was switched off when getting the neutral - earth shocks, and hadn't fired the PV generation up when I was monitoring the later most extreme phase voltage differences. Their regular electrician had also been in at some stage to apparently rebalance the phases.
Unfortunately I only went in there to set up some monitoring kit this afternoon, and was being rushed to get out of the door at the end by their guy wanting to lock up when I spotted the last voltage readings, so didn't have time to actually check or do anything other than turn the inverter circuit off that I'd been working on in case I'd done something on that circuit.
ps yes I'm only short course trained, but have been working alongside a proper spark for the last 4 1/2 years who did all the wiring and testing, I was just setting up the monitoring kit for the solar in a little single phase sub board we'd already installed, as I'm better at that stuff. Planning to go back first thing Monday morning with our spark to fully test it and work out what's going on, but I'm trying to work out if we actually should be trying to get hold of the owner to get in on Sunday before they actually fire up all the machinery on Monday morning.
Any thoughts appreciated
Situation is a factory unit, 3 phase, TN-C-S, 100amp per phase supply, at the end of a fairly long supply line at the extremes of it's capacity, and I think with several other units being fed from the same line prior to the factory, the DNO installations is probably 50+ years old.
Symptoms are
1 - extreme imbalance of the phase voltages, with the phases eg 250, 238, 220V respectively during the day when the 3 phase printing machines were operating relatively well balanced load, then just as I was being ushered out of the door with all the machines off and only a small single phase load for office lights, fridge, etc, I went to check why our inverter wasn't working and the voltage readings were showing something like 280, 250 and 180V respectively.
2 - Getting a few minor shocks between neutral and the earthed metal trunking on a little sub board with the 3 pole breaker feeding that board switched off.
We'd fitted a 30kWp solar PV system a month or so ago, but this was switched off when getting the neutral - earth shocks, and hadn't fired the PV generation up when I was monitoring the later most extreme phase voltage differences. Their regular electrician had also been in at some stage to apparently rebalance the phases.
Unfortunately I only went in there to set up some monitoring kit this afternoon, and was being rushed to get out of the door at the end by their guy wanting to lock up when I spotted the last voltage readings, so didn't have time to actually check or do anything other than turn the inverter circuit off that I'd been working on in case I'd done something on that circuit.
ps yes I'm only short course trained, but have been working alongside a proper spark for the last 4 1/2 years who did all the wiring and testing, I was just setting up the monitoring kit for the solar in a little single phase sub board we'd already installed, as I'm better at that stuff. Planning to go back first thing Monday morning with our spark to fully test it and work out what's going on, but I'm trying to work out if we actually should be trying to get hold of the owner to get in on Sunday before they actually fire up all the machinery on Monday morning.
Any thoughts appreciated