Discuss Very high Zs reading in the UK Electrical Forum area at ElectriciansForums.net
M
mspms
Good evening all. I wonder if anyone could give me a steer as to why I am getting very high Zs readings. I have been testin a circuit that has a R1+R2 of 0.23 ohms but I seem to be getting Zs reading on L-E of + 40ohms. L-N is coming in at 0.2ohms. The incoming fuse is a 63amp BS1361 an RCD main switch protecting all circuits. All other tests are fine. I am wondering whether it could be my meter not reading correctly on the Zs test. Any ideas?
Thanks all.
try taking as reading on the L busbar. if that is high, then it's due to internal resistance of RCD and/or MCB. flick them on and off a couple of times. if that reading is OK, try at the terminals of the socket, not the front. try flicking the socket switch/es on/off.
Never considered that but will remember it for future reference!!
Thanks for your suggestion I will give it a go. Just to add more pain, I thought I would try a reading from a socket in my own home and again I'm getting +40ohms. Just coincedence?
What are you using to test the socket? Have you tried testing at the terminals on the back?
Sorry teletrix. It was a long day. I gave up and came home. The house is empty at the moment so no chance of any mishaps!
My Ze was really low at 0.09ohms. My meter has just been calibrated and it is a TN-C-S.
- - - Updated - - -
I'm using my 3pin plug and leads.
Batteries going down? Bad contacts on the three pin plug? Dodgy terminations, any load on the circuit? (mainly an inductive might cause a false reading) What make of RCD is it?
Reply to Very high Zs reading in the UK Electrical Forum area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...