My question is what would I set the overload to on a soft start. Do I use the FLC on the name plate or that value /1.73 as what it says on the soft start.
Thank you for your help in advance guys.
9402684A-3888-4242-89F8-1D9A9E7754B5.jpeg
 
The setting of soft start unit all depends on how it has been wired and from your photo I can’t tell.
Is the soft start wired as a direct on line, I.e 3 wires to the motor or is it inside a delta loop - 6 wires to the motor?
If it is 3 wires, you set it to the current rating of the motor plate, if it’s inside the delta loop you set it by dividing the current rating on the motor plate by 1.732
 
  • Like
Reactions: Jako13!

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Maintenance Electrician

Thread Information

Title
What do I Set the overload to on a soft start
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Jako13!,
Last reply from
Andy-1960,
Replies
1
Views
1,297

Advert