O
Octopus
Required by buyers solicitor.
I appreciate you taking the time to answer.
Did you organise the EICR and if so how long was the spark onsite and how much did they charge?
I think it's ironic that they're quoting 18th edition regs, at the same time writing the report on out of date forms. They state complies with BS3671:2008 revised 2015. Aren't the new forms as revised 2018?Well then that's a load 9f ******** in my opinion.
I'd ask them to re-do the report with a proper description of the problem they have identified.
I did, and they managed to get me in same day. About £140Did you organise the EICR and if so how long was the spark onsite and how much did they charge?
Sorry, about an hour and a half. Had all the kit.I did, and they managed to get me in same day. About £140
3 bed, 90 minsHow big is the property and how long were they on site?
3 bed, 90 mins
As my missus tells me, looks aren't everything.On the basis of the photo of that CU I cannot believe there aren't more observations listed, if I got that EICR as a buyer I would be sending my own electrician around. I normally get instructed by the buyer not the seller!
There is no such thing as a fire rated consumer unit.
I dunno....Went to this previous year...(mcbs cleaned before the pic was taken) contained the situation.
Not sure you will get RCBO ‘s in that unit ....especially near the main switch.
Yep spot! on the neutral bar is right above the mcbs!
Oh look I just spotted the sarcasm flying over your head....That is a dist board constructed from non combustible materials, not a fire rated dist board.