Hello guys,
Do you do Earth fault loop impedance test for lighting circuits during periodic inspection ? do you measure it at the lighting point? what is the percentage of lights you test?
Thanks alot in advance
 
Yes you do like all circuits,@ furthest light & several to check readings.
% depends on client,usually on a domestic it’s reasonable to check all circuits.
 
i just do R2 on lights
yeah, I am not sure it if it necessary to to it. on the GN3 guideline, it has been mentioned the recommended points to be tested are at:
- origin of the installation
-distribution boards
-accessible socket outlets
-extremity of radial circuits
[automerge]1571029063[/automerge]
On the GN3 guideline, it has been mentioned the recommended points to be tested are at:
- origin of the installation
-distribution boards
-accessible socket outlets
-extremity of radial circuits
 
the last one..... the extremity of a radial includes a lighting circuit. so it would appear that recommended is all accessible sockets (on a ring) or last point on a radial (socket, lights.or other radial).)
 
The reason for doing this test is to verify that Zs is low enough and at the time of earth fault, current would be high enough to trip to breaker(MCB).Correct? Where I work ( in Dubai) we have 100mA RCDs for all lighting circuits. So practically, if there is any earth fault, the RCD would detect and remove the fault much quicker than MCB and it would not let the current reaches to the MCB tripping point. So I am not sure how useful this test is!
 
it would not let the current reaches to the MCB tripping point.
An RCD will not limit the current, but simply provide disconnection where the rated residual operating current (well actually between half and all of the rated residual operating current) is exceeded.
 
An RCD will not limit the current, but simply provide disconnection where the rated residual operating current (well actually between half and all of the rated residual operating current) is exceeded.
I agree but the purpose of testing Zs on lighting point and checking the values with Zs of protection device ( MCB in our case) is useless because the RCD will detect and remove the earth fault much quicker than MCB. Means even if the Zs value is higher than values mentioned in the BS7671 Table, the RCD will disconnect the earth fault . Am I wrong?
 
Means even if the Zs value is higher than values mentioned in the BS7671 Table, the RCD will disconnect the earth fault . Am I wrong?

The RCD will disconnect quickly at impedances well above the Zs needed for the MCB, so in that sense you are right.

But equally if the Zs values is higher than what was designed (or reasonably expected for the type of circuit and size of installation) then it points to something going bad. Could be a loose joint, cable near the point of fracturing, bad repair with seriously under-spec cable, etc, which should be investigated.
 
So practically, if there is any earth fault, the RCD would detect and remove the fault much quicker than MCB
Yes, practically

BUT

an RCD is only an additional protection device. The circuit should be designed so that an MCB/fuse will disconnect the supply in the event of an earth fault. So the circuit must correctly meet the EFLI criterea.
 
an RCD is only an additional protection device.

This is a very important point.

An RCD (and the equivalent section in an RCBO) is an order of magnitude more complicated than a MCB and far more likely to fail "unsafe", hence the periodic testing that is specified (though I doubt most folk do it).
 

Reply to Earth Fault Loop Impedance Test for lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
966
  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
1K
  • Question
(2.4-0.4)×1.2+0.4 = 2.8ohms
Replies
4
Views
1K
Hi David. I'm currently doing this same design project from home. Can I ask you a question? When working out the design current for the circuits...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks