- Jan 3, 2017
- 4,970
- 10,455
- 18,688
- United Kingdom
- Business Name
- SparkyChick
I fully agree that this is incorrect and should not have been done.
But having said that what are the apparent dangers? I don't see any particular danger attributable to this.
The definition of a circuit is based around everything that is connected to a single way in a distribution board, so this would still count as one circuit, although it is nom-standard.
@Pete999 , Dave has summed up my own personal view to a T.
If both of the rings are correctly installed and the cables sized correctly, then I'm struggling to see how this arrangement would be any more dangerous than each of them connected to their own MCB, sure from an isolation point of view it's less than ideal, but from a safety perspective I don't see how it's any less safe than a ring final running from it's own 32A MCB. If you were talking two ring circuits supplied by two MCBs with one leg of each ring in each MCB, that's another matter (have seen this and nearly got bit by it, thankfully my chicky sense started tingling and I did another check at the socket I was working on).
And I'll reiterate what I said... I personally wouldn't do it, except as maybe a temporary solution to restore supply in the event of say an MCB or RCBO failure. But I think it's an interesting thought exercise because I'm not sure what regulations it would be breaching. The closest I can come to is largely dependent on how you define circuit.
Just a point.
Two rings or not, in general, what are FIRST thoughts on four (or more) cables in a circuit breaker terminal, whilst carrying out an EICR?
How long is a piece of string, maybe?
Absolutely, it's not good, and it would be a C3 from me, unless there were clear signs of bad connections (loose cables, heat damage etc.) in which case it would be a C2. My reasoning... does it present a danger now or would it present a danger if something else happened? Potentially it might, but so would any ring final circuit and I'm thinking broken or poor end to end continuity or some other error in installation.
But like I said, I'm just curious about peoples thought processes and reasoning. We can't remember everything and we certainly can't know everything so it's an interesting topic for debate
[automerge]1588094893[/automerge]
right or wrong what's the common response to finding a Ring on a 20A MCB or wired in 4mm??
Could be a long cable run, the 20A MCB could be a left over from a broken ring when someone downgraded it to be safe, the 4mm could be there because the Zdb at the source of the circuit was too high for 2.5mm to cut it from a Maximum Zs perspective, or in extreme cases even a maximum NL loop impedence perspective.
But if it was safe and compliant, I'd just be asking myself why?
I did a rewire job last year and ran a ring in 4mm. It was a mistake on my part... I picked up the wrong reel and just cracked on. Was a costly mistake, but hey ho