The thing is, you won't always be able to find a reg to say something is wrong. Otherwise where would it end? Do you have regulation 3.23.1.0.1 that says you cant have 18 RFCs in one MCB?
Reactions: SparkyChick
Reactions: James
...or seven 1.5 twin's in a rose.
  • Funny
manufacturors instructions.
terminal capacity of 32A mcb is 25 sqmm
18 rfc at 2.5mm is 90 sqmm
so yes it is against manufacturors instructions and outside of the specifications of the ocpd.
that's not to say that you cant find a breaker that will take all those cables.
I wouldn't fancy trying to terminate them correctly though!!
:D:D:D:D
I absolutely 100% agree, which is why topics like this are good ones for discussion.
From a technical perspective I can find no reason the situation would breach the regulations but I just feel it's wrong.
For me, these are some points about why I think it's wrong....
It increases the inconvenience in the event of a fault or when works need to be carried out on one of the rings. It also raises some interesting questions about the testing and recording side of things.
Sure we can test each ring, but how do we record that? Separate lines on the cert or just use one line and record the worst case? If we do the latter we won't have records for a major section and thus we won't be able to determine if there has been any deterioration until perhaps there is a significant change.
What is the next spark going to assume about the installation? RFC + two spurs maybe, unless there is a note on the certificate. I think fault finding on it has the potential to be complete nightmare. Will they assume it was two spurs + a ring that have been bodged together by someone and then set about trying to 'fix' it?
This is the sort of thing that is wrong with it, not the current capacity (as that is not different from a bigger single ring), but the fact it is hard to test and unexpected/unconventional for any future fault finding or repair work.
Nobody expects the Spanish ring final circuit! Among our methods are multiple connections and a fanatical...
Expats do it and Twin and Earth is illegal the main problem probably in Spain would be your insurance maybe an insurance company might not be happy with OPs arrangement again could they prove it is against any rules or unsafe.
In France where you have to follow local council rules you could get into quite a bit of trouble.
SC I have stated my point of view, and although an interesting post I really have nothing more to say on the subject, you questioned the dangerous statement, which is your prerogative, I just think sticking two separate systems on one OCPD forming one circuit out of two systems is inherently dangerous, I have no other arguments to continue, what next a lighting system added to a RFC circuit OCPD? or vice versa?
I don't think you can leave it there Pete, I respect your point of view but you have to state exactly what you believe the danger is here, simply saying it's dangerous without giving reasons is not very helpful to those who don't have your experience and are wanting to understand.
Your point about a lighting system added to a RFC circuit is illogical as Spock might say, a lighting circuit is normally wired in 1.0 or 1.5mm cable, and connecting that directly to a 32a OCPD would be a breach of regulations and potentially dangerous because the cable would not be adequately protected against overcurrent. There is a sound reason for not doing so.
I've carried out Continuity tests on all four conductors this evening to find it is 2 RFCs, both sets of circuit conductors have now been marked so they can be identified correctly. Also on closer inspection I've found an sorry looking 32amp breaker in amongst a load of other rubble which could of potentially been from the spare way in the Consumer? Orignally it looks as if these RFCs were both on there own MCB. Going forward I'll purchase a new breaker and seperate these two circuits to there own supply.
Just thinking the reasoning behind putting 2 RFC on one 32a , just maybe there was an interconnection between the 2 circuits, and some lazy so n so could not be bothered to fault find it.
I THINK I GUESSED RIGHT FOR ONCE!!
it could even be that originally it was 2 circuits.
failed mcb was removed and temporary supply taken from the one next to it.
late night tempory fix that never got finished off?
Gave you a funny
It does not meat the regs BUT. if you exceed the loading I will be surprised but if you do the breaker will trip, ie doing its job.
@Ed Evans , as I've stated already in this thread I'm interested in peoples thought processes on things like this. How do you conclude that it's a breach of the regulations?
Outside of the UK you would not use a ring final circuit because you don't have fused plugs.
Without fused plugs your breaker has to be sized for the appliance cable, probably no more than 1mm so MCB no more than 10-16A. If you are limited to, say, 16A on the circuit, no more than a couple of sockets. If only a couple of sockets, then why a ring as a radial is perfectly suited for that case?
If you cannot make a reasonable technical argument to support your statement about it being dangerous then how can you expect anyone to take you seriously?
When people come on the forum saying that someone has told them their electrical installation is dangerous we always advise them to find out from that person exactly why it is dangerous and to get references to regulations.
Making a statement about something being dangerous without backing it up makes it appear that you have nothing to back it up and are condemning something as dangerous through a knee jerk reaction rather than any technical consideration.
All ifs and buts I know.
So if tested and it is two good rings and all sockets on both rings/floor area dont constitute an overload/regs breach then crimp up one leg from each and put the other in the OCPD.
one ring = resolved.
The OP has the smell of a short term fix that was never returned to with a shrug "well it's ugly but it aint going to kill anyone"
Not so anything on the house owners side of the meter is the owners responsibility Consuel is not interested unless it's a new supply and then you have to apply to Enedis and Consuel will inspect, as long as you have one socket and one light fitted correctly they will instal and issue a certificate of conformity, only on re-sale or change of tenant is any type of inspection carried out on the whole installation and even then it's a tick box exercise.
Ring main.
JKMRK1,
Risteard,