E

Edward67

Hi

I have just had my boiler replaced which was a potterton suprima 60l. Heat only boiler as it kept cutting out.
I have had a vailent ecofit 425 fitted by engineer but now my pump is running continuously.
This wasn't the case before.
It's s plan with two heating 2 port valves and 1 hot water two port valve.
I have two stats and they are both 3 core.
The boiler as far as I can tell has live neutral and earth the a second cable linked with live which. I think goes to the pump and another in rt.
I have checked boiler setting and they Re set too intermittent with 5 min over run.
The fitter says he doesn't know and has asked vailant to attend at my cost.
Help appreciated. I am an electrician but my heating side is limited.
Ideas most welcome.

Thanks
 
Is the boiler firing without being called to?
It sounds like he has left the link in on the 24v RT which is a common mistake.
 
Is the boiler firing without being called to?
It sounds like he has left the link in on the 24v RT which is a common mistake.
Hi thanks for reply.

The link has been removed and the heating is working on programmer as you would expect.
The pump is even on if I disconnect the programmer because the L and RT cable in the boiler are fed to connectors behind programmer no to the programmer itself.
 

Attachments

  • 16107446500263795102731087085778.jpg
    16107446500263795102731087085778.jpg
    238.2 KB · Views: 58
Hi thanks for reply.

The link has been removed and the heating is working on programmer as you would expect.
The pump is even on if I disconnect the programmer because the L and RT cable in the boiler are fed to connectors behind programmer no to the programmer itself.

Is the boiler firing without being called to?
It sounds like he has left the link in on the 24v RT which is a common mistake.
 

Attachments

  • 16107448484653869851361522065316.jpg
    16107448484653869851361522065316.jpg
    333.3 KB · Views: 48
  • 16107449191296734246929564605525.jpg
    16107449191296734246929564605525.jpg
    351.1 KB · Views: 52
It all worked before boiler was fitted.

Thank you. For help.
 

Attachments

  • 16107449446515592402547468393315.jpg
    16107449446515592402547468393315.jpg
    318.1 KB · Views: 57
If, as you say, the second cable in the live terminal goes to the pump, then of course the pump will run continuously.
 
  • Agree
Reactions: PEG
If, as you say, the second cable in the live terminal goes to the pump, then of course the pump will run continuously.
So how do I rectify as heating engineer doesn't know. The only boiler connections are live neutral earth and RT.
What is different between this boiler and old boiler. I never saw the connections on the old potterton. Would it of has a pump feed on it?
 
You'll have to work through the wiring Edward, trace it and make a drawing. Does the extra cable go to the pump or not? it should be easy to prove one way or another. Does it go to the room stat? if not where is the room stat cable? where's the junction box? You need to find all these things before you can find the problem.
If you do a simple schematic drawing of where all the conductors go, you'll be able to sort this.
 
  • Like
Reactions: DPG
So how do I rectify as heating engineer doesn't know. The only boiler connections are live neutral earth and RT.
What is different between this boiler and old boiler. I never saw the connections on the old potterton. Would it of has a pump feed on it?
really! The heating engineer doesn’t know.
he shouldn’t be a heating engineer then.

The Pump needs to be wired into the switched live and come on when heat is called for. Possibly there is somewhere in the boiler for a separate connection to allow over run, but impossible to diagnose from afar.
 
It all worked before boiler was fitted.

Thank you. For help.
The pump needs connected to the pump terminal block in the boiler, at present there is nothing connected to that block.
 
The pump needs connected to the pump terminal block in the boiler, at present there is nothing connected to that block.
Good eyes 123. I couldn’t see the pump terminal in boiler. Where is it?
 
  • Like
Reactions: loz2754
Good eyes 123. I couldn’t see the pump terminal in boiler. Where is it?
X14 - it's hiding under the mains cables, obscured by the brown & blue wires.
 
  • Like
Reactions: Edward67 and Timbo
X14 - it's hiding under the mains cables, obscured by the brown & blue wires.
Wow good spot. Couldn’t see it even after you pointed it out. The wife had to point it out to me.
I still find It hard to believe the heating engineer didnt know how to do this.
 
  • Like
Reactions: DPG
really! The heating engineer doesn’t know.
he shouldn’t be a heating engineer then.

The Pump needs to be wired into the switched live and come on when heat is called for. Possibly there is somewhere in the boiler for a separate connection to allow over run, but impossible to diagnose from afar.
Thanks for reply.
I think it needs a spdt timer relay fitting to control the pump unless the new boiler can be retrofitted.
 
Thanks for reply.
I think it needs a spdt timer relay fitting to control the pump unless the new boiler can be retrofitted.
The pump terminations have been identified in post 11,12 & 14. No retro should be needed. Your gas installer should know this. Consult him.
 
  • Like
Reactions: suffolkspark
Thanks for reply.
I think it needs a spdt timer relay fitting to control the pump unless the new boiler can be retrofitted.
It does need a timer relay to control the pump, and one, in some form or other, is already built into the boiler, but it won't do much unless the pump is actually connected to it!
 
  • Like
Reactions: Deleted account
123 did well to spot that, I couldn't see it, even after he said it was there. I do now.
What I would say is be carefull. The blue has some black tape on it so I doubt that it's a neutral.
My guess, and it's just a guess, it will need to be proved. Is that the extra cable is the switched feed for the heating and the pump live feed from the connections that 123 identified.
 
  • Like
Reactions: Deleted account
Going back to your original post. valiant are coming out at your cost.
seriously that engineer needs to pay for this not you. He should know better than us sparkies.

try the plumbing forum. They will slate the engineer for not knowing.

someone on here should give you a link to them.
 
  • Like
Reactions: DPG
Going back to your original post. valiant are coming out at your cost.
seriously that engineer needs to pay for this not you. He should know better than us sparkies.

try the plumbing forum. They will slate the engineer for not knowing.

someone on here should give you a link to them.
I agree, I'd get in touch and cancel, it can't be much.
You said that you think the extra brown is to the pump, then take it out of the live terminal and put it into the pump live, that will probally sort it.
 
  • Agree
Reactions: Avo Mk8

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Central heating pump on continuous
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
Edward67,
Last reply from
Deleted account,
Replies
34
Views
8,147

Advert