Moses, please before this develops in to bloodshed. Will you please go away and check your facts.
Your becoming what we refer to as a TROLL. Anything to start an argument.
This discussion could have reach a successful concussion ages ago had it not been for your misinformed, inane comments.
 
  • Like
Reactions: 1 person
Moses, please before this develops in to bloodshed. Will you please go away and check your facts.
Your becoming what we refer to as a TROLL. Anything to start an argument.
This discussion could have reach a successful concussion ages ago had it not been for your misinformed, inane comments.

Nah. 1st rule of trolling is, start a contentious thread, then make no further posts.
He could be an amateur of course.
 
  • Like
Reactions: 3 people
Moses, please before this develops in to bloodshed. Will you please go away and check your facts.
Your becoming what we refer to as a TROLL. Anything to start an argument.
This discussion could have reach a successful concussion ages ago had it not been for your misinformed, inane comments.

Not happy about your comments but I will give you benefit of doubt.

Please correct me, and point out which misinformed comments?
 
Last edited by a moderator:
not if there faulty....it may appear that they have......

OP's end to end measurements indicate to me that there are no dodgy socket connections.
The difference (too large) between his R1+R2 and Zs measurements rule out non zeroed leads.
There's something else going on here. As someone already asked, where did he take his Ze.

As for the original Q about the one high reading, $%& knows.
 
OP's end to end measurements indicate to me that there are no dodgy socket connections.

Had it before Archy, where the end to ends were fine, and the socket connection itself was iffy, caused by dampness if I recall.
 
Had it before Archy, where the end to ends were fine, and the socket connection itself was iffy, caused by dampness if I recall.

Is there an RCD (not reading through all this again!). Dubious 'no trip' readings?
Maybe he should retry Zsing with the RCB bypassed.

Personally, I'd pass it.
 
You could try a new CB, may be the Cb is faulty and giving a hi Z ?

May be link it out temporarly and the do a test to see if you get anywhere?
 
Is there an RCD (not reading through all this again!). Dubious 'no trip' readings?
Maybe he should retry Zsing with the RCB bypassed.

Personally, I'd pass it.

Yes I believe there is, this was my one of my first thoughts (dodgy no-trip reading) but the OP's other readings would have been similarly affected I would have thought.

The end to ends and crossover readings were reasonable, it can only really be at the interface between cables-socket, or socket-meter on that one S/O, the ring was extended to that S/O, ie. not a spur.

Edit: the high Zs reading S/O was also an outdoor type.

Edit II: the OP also said it was measured at the back of the S/O as well as with the plug adaptor
 
Last edited by a moderator:
Yes I believe there is, this was my one of my first thoughts (dodgy no-trip reading) but the OP's other readings would have been similarly affected I would have thought.

The end to ends and crossover readings were reasonable, it can only really be at the interface between cables-socket, or socket-meter on that one S/O, the ring was extended to that S/O, ie. not a spur.

Edit: the high Zs reading S/O was also an outdoor type.

Edit II: the OP also said he measured at the back of the S/O

I was going to suggest something for a moment there, fortunately the alcohol has taken total effect yet...
 
The only thing I can think of is that the connection between the terminals in the socket and the incoming cable(s) is poor and that the test at the back of the socket was connecting to the terminals and not directly on to the cable. Re-terminating the cables in the back of the outside socket may resolve the reading, other than that, based on the information given, there is a physics anomaly on the ring!
 
  • Like
Reactions: 1 person
^^^^^^^

That's what I said for the OP to check, many posts way back in this thread Rich, lol:rofl:
 
Last edited by a moderator:
  • Like
Reactions: 1 person
^^^^^^^

That's what I said for the OP to check, many posts way back in this thread Rich, lol:rofl:
You did indeed; I am far too slow, I have just reread the whole thread(!!!) and saw your post, :oops:.
Still doesn't explain the highish Zs overall but would make it compliant for the MCB.
 
Hi Rich,

The OP never said if he did the (R1+R2) dead tests at each socket, I did ask.

The overall end to end and crossover readings r1 and r2 and R1+R2 were about correct and not too far out when added to the Ze.

My next move would have been to temporarily put the pairs of the Hi Z S/O conductors into three seperate Chock blocks or similar to see if I got more sensible/expected readings, and then replace the S/O if necessary.

I have had it before where the conductors have been twisted together giving reasonable end to end results, but poor at the S/O (slack terminal screw), or the odd time where the S/O terminal has suffered due to dampness/corrosion and gave poor or high readings, yet the end to end readings have been again reasonable.
 
Last edited by a moderator:
Up date. Have found that when my meter says that it has zeroed the leads on screen that is not always the case, but when I turn off meter it should reset.Infact it still says that the leads are zeroed when I switch it back on but when I do a little check the leads are not nullified until I zero them again. Lesson learned and this may solve the problem will retest tomorrow.
 
Up date. Have found that when my meter says that it has zeroed the leads on screen that is not always the case, but when I turn off meter it should reset.Infact it still says that the leads are zeroed when I switch it back on but when I do a little check the leads are not nullified until I zero them again. Lesson learned and this may solve the problem will retest tomorrow.

Oh well, a decent outcome to one of the worst-answered threads I've ever seen here!
There's an old saying "Sometimes it's better to keep your mouth shut and look stupid than to open your mouth and prove it" ;)
 
Last edited:
Up date. Have found that when my meter says that it has zeroed the leads on screen that is not always the case, but when I turn off meter it should reset.Infact it still says that the leads are zeroed when I switch it back on but when I do a little check the leads are not nullified until I zero them again. Lesson learned and this may solve the problem will retest tomorrow.


Nice one son!!!!
 
never had these problems when all we had was avo 8's.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Socket Zs High
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
89

Advert

Thread statistics

Created
AdieB,
Last reply from
Des 56,
Replies
89
Views
16,680

Advert