I’m installing 20KW of Solar on my Barn roof,

The barn is fed from a 3 phase supply originating at the house which is 80 meters away.

I’ll be installing some 35mm 4 core to minimise the losses to <1% volt drop between the barn and the point of supply located at the house.

The Earthing at the Cut Out at the house is TNC-S fed from a PME.

In The Barn is a consumer unit, 3 phase stuff, Lathe, Welding, car lift and some single phase consumers.

Located at the house is another 3 Phase Board, with single phases feeding the House, the Annex (A small bungalow) and some Lighting for stables and outdoor sockets

I’m using 2x Single phase invertors due to the loads being unbalanced and there being only two main consumers, House and Annex.

My question is what earthing arrangement should I use at the Barn, it’s 80 Meters from the point of supply, is a consumer, but when the Solar Panels are working it’s a generator?
 
Assuming the invertors will only ever be working in a grid tied mode, and assuming your bonding requirements are covered then TNCS.
 
Thanks for the answer, it is what the general consensus was here, but not being a house electrician just wanted it confirmed !
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Norfolk UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Barn Earthing for Solar, 80 Meters from Cut Out
Prefix
Solar Panels 
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Clarky the Sparky,
Last reply from
Clarky the Sparky,
Replies
2
Views
1,433

Advert