Discuss calculating demand in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
a local pub i do alot of work for wants to build 6 pod style holiday lets in its beer garden and has applied to western power to see if the existing supply can cope with the demand
the existing supply is 2 phase with a 200 amp fuse in each phase leading to a busbar system. ive been asked to calculate for the owner what the maximim demand for these 6 pods will be in total

hes given me the following info

Building requirement: 7.5kw
3.5kw Space Heating
3kw Water Boiler
1kw Lights (LEDs)

Appliance requirement: 8.0kw
1kw Microwave
1.5kw Kettle
3kw Oven
0.5kw TV
1kw Hair Dryer
1kw Iron

for me i'd of said the heater and water boiler are likely to be on at the same time and maybe an appliance or 2 so i'd allow 8kw per pod but 8x6 pods would be 48kw? can i apply any further diversity or is that the figure i'll have to give??

many thanks rob
 
Why would the water boiler and heater be on at the same?

Will they be occupied all year round?
Will they all be occupied at the same time?
 
i'd take a guess at any business wanting to make money would like all 6 let every week 12 months a year but in reality in will be busier in the summer

why wouldnt the hot water be on for a shower etc while they have the heater switched on in the main room?
 
i haven't been told the make/model of anything being used. the information i was given im assuming was supplied to the owner from the manufacturers of these pods. as far as i know these pods arrive complete and i will be just connecting them up. with regards to the water boiler i'd guess at it being an unvented cylinder so they can get a powerfull shower off it

i know the original quote for installing a new 3 phase supply was about 30 grand plus vat which is why their trying to get away with taking supplies off the exisiting 2 phase supply. apart from the kitchen which is mainly kitted out with applainces which use gas bottles and a few electric fryers/plate warmers the pub isnt huge and doesn't pull alot of electric
 
i would agree most of the time there would be hardly any draw but i'm thinking of the times when maybe a group hires all 6, goes out surfing for the day and the first thing the'd do when they came back in an evening would to be to put on the heating and all have a shower/put the oven on
 
i would agree most of the time there would be hardly any draw but i'm thinking of the times when maybe a group hires all 6, goes out surfing for the day and the first thing the'd do when they came back in an evening would to be to put on the heating and all have a shower/put the oven on

That would be a short term peak load then wouldn't it, not quite the same as the maximum average demand
 
thats a good table for calculating demand for a property but i'd end up with 60-80kw using it to the letter of the law depending on how generous i was beiing which seems unrealistic for 6 small holiday pods in the beer garden of a seaside pub
 
IMO for the immersions you could say allow 100% flc for the 1st two huts then 25% for the other four huts as all won't be on at the same time plus will have thermostatic control etc. then 66% of lighting across all six huts, repeat the process for cookers, heaters etc then divide the final figure by 6 so you roughly know what you will be looking at for each hut.

100% for the sockets in the 1st hut then 40% across the other huts etc
 
Last edited:
a local pub i do alot of work for wants to build 6 pod style holiday lets in its beer garden and has applied to western power to see if the existing supply can cope with the demand
the existing supply is 2 phase with a 200 amp fuse in each phase leading to a busbar system. ive been asked to calculate for the owner what the maximim demand for these 6 pods will be in total

hes given me the following info

Building requirement: 7.5kw
3.5kw Space Heating
3kw Water Boiler
1kw Lights (LEDs)

Appliance requirement: 8.0kw
1kw Microwave
1.5kw Kettle
3kw Oven
0.5kw TV
1kw Hair Dryer
1kw Iron

for me i'd of said the heater and water boiler are likely to be on at the same time and maybe an appliance or 2 so i'd allow 8kw per pod but 8x6 pods would be 48kw can i apply any further diversity or is that the figure i'll have to give??

many thanks rob

I think your figure of 48kw is pretty spot on.
 
Last edited:

Reply to calculating demand in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This isn't sitting right with me. So if I rock up at a house with a 60A suppliers fuse, it has a dear old Wylex with 1 RFC 30A (no diversity) 1...
Replies
12
Views
3K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
791
I have been asked to do some work on a large 25 room mini mansion spread over 3 old properties made in to 1 with 6 consumer units on a single...
Replies
14
Views
3K
Hi all, I wonder if you might chuck in your 10 cents worth on this on? I have been asked to install electric heating in an office up on the 4th...
Replies
18
Views
3K
Toneyz
T
Hi All and thanks to those who take the time to reply. My concern is the amount of current the building could pull in use. I will try and give...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock