Hi All and thanks to those who take the time to reply.

My concern is the amount of current the building could pull in use. I will try and give some salient facts.

160 flats over 8 floors. The landlords areas per floor consist of 20 x 20W led lights and several occasional cleaners sockets hence a few amps per floor - I'm not worried about these.

Other noteable loads are...

The laundry has 10 x 25A washer / driers.
The lift is 3 phase and is rated t 30A
The water is pumped to all floor and the pump can draw 60A.

Each flat (160 of them) has seven circuits. Hob (4KW) - 20A breaker. Heater (1KW) - 6A breaker . Ring-32A breaker . Lighting 6A breaker. Fridge-6A breaker. Shower (7.5KW)-32A breaker. Water heater (3KW) - 16A breaker.

The incoming supply is a 400A 3 phase PME, so 1200A total.

As the flats are "all bills included" the occupants will think nothing of leaving the heats on all the time and a 1K heater never thermostatically switched off as the rooms are so big. So 160 a 4A (1KW loading) = 640A. That's half the supply taken already and would only leave 3.5A per flat.

When I have raised my concerns I have been told not to worry but I do.

With diversity you're looking around 60A (someone may correct me on the exact figure). 60A x 160 flats = 9600A. That's a bit over a difference from the incoming 1200A.

Perhaps there are special calculations as all flats may not be in use at the same time etc. But with the info I have given can person(s) put at mind at rest and confirm the 1200A supply is more than capable?

Once again, cheers for reading and for any reples.
 
are any OCPDs tripping/blowing?
 
Why are you concerned.
 
A clamp ammeter or 3 might resolve some of the concerns.

I'm sure that the National Grid managers fear the day everyone leaves at least 1 light switched on.
 
Is this concern at a planning stage of the job,? Or is the building running in use.. sounds well undersupplied to me
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Load concern
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
bottlebasher,
Last reply from
Wilko,
Replies
6
Views
1,643

Advert