Hi Guys
Just been wondering, why dont we test circuit breakers? There's testing equipment that does this on an industrial scale but how come its not applicable in the household? Do we just have to trust the manufacturers guarantee, as ive recently fitted a CB new and it wasnt functioning correctly, ie it wastripping too soon.
Thanks
 
It was tripping at half its rated value, basically it was a 30A CB and was tripping at 16A. I had an ammeter measuring the current draw and just used appliances like kettle and toaster as I was also checking to see if these were faulty.
 
The test equipment to test MCB's would cost far more than the most expensive MFT you can buy. Seeing as MCB's are generally going to be cheap to just replace, it makes far more sense to go down the replacement route!! Unlike say RCD devices, MCB's are generally taken as being a very reliable protective device.
 
If you consider the MCB to be faulty just change it out for a new one. Why muck about with it?

The existing unit may have taken a short circuit condition in it's past and now no longer functioning to it's type/rating specification....
 
It was a brand new board i had put in and it was the kitchen circuit that was tripping so I first assumed it to be a faulty appliance. I had every part of the installation switched off except for that circuit and had a clamp ammeter on the mains tail as it was easiest to get the clamp onto.
I wasnt taking times when it was tripping but I would say it varied between 5 and 14 seconds.
And yes its what the other post(under the same title) said that it is too expensive for the equipment when its generally easier and cheaper to replace what are normally very reliable.
 
You also have to take in to account that to correctly test a MCB it wouldn’t be fit for continued use. Testing the MCB would involve using several points on the exponential time curve. OK at the lower currents although it could take several hours, at the maximum prospective short circuit current the MCB wouldn’t be fit for continued reliable use afterwards.

The manufacturers do batch testing, say 1 in every 50.

There's also the minor point, they can afford to throw them away, can you?
 

Reply to Circuit breaker testing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top