Can you get 2 x 6mm in the back of the socket outlet?
Can you get 2 x 6mm2 in the terminals even?
Sorry, I don’t quite understand this bit. You mean if I put a socket on the 6mm distribution supply cable I won’t be able to add new circuits to the shed CU?
thank you for helping me
Best get an Electrician to help you with the installation.
It was not obvious from your original post that it is already supplying a CU!
As a sub-main in SWA you have more choices than if it is a final circuit. Specifically you don't need RCD protection on SWA (as the armour protects against cable penetrating damage) and as a sub-main you are allowed up to 5s disconnections times (so you can use a fused-switch to feed it and achieve selectivity with the downstream MCB/RCBO).
Basically having selectivity means that a fault on a final circuit will only trip the local CU's MCB/RCBO, and not take out the whole lot. That is a special risk if the shed is used as a workshop and being plunged in to darkness a safety hazard!
Once you put a socket on the 6mm sub-main it must have both 30mA 'instant' RCD protection and 0.4s fault current disconnection times. At that point you won't be able to achieve any useful selectivity on either earth leak faults or on over-current faults.
Now that may well be how it is currently wired, and if you are OK with that then fine. But if adding circuits to the CU in the future, which I think is notifiable work, you may find most electricians are unhappy at the inability to design/modify for adequate selectivity (as required by the wiring regulations) without having to undo your work.
[automerge]1595015006[/automerge]
Basically you would be well advised to follow telectrix's advice in post #6 and simply run another feed to an outside socket from the internal socket circuit.
If you want proper selectivity it would be notifiable to change the overall CU configuration, but simply running your new socket feed to the existing MCB would make that job much easier in the future. Then any electrician would have the cable there to put it on a separate circuit, RCBO for all if needed, and change the sub-main feed to a fused-switch.
But again that is for future consideration.
Hi,
thank you for the advice.
The sheds essentially a storage shed and she just wants a couple of outdoor lights and a couple of outdoor sockets added. She’s not going to be wanting to spend extra money for future workshop possibilities as she’s not looking to ever sell.
Even if I could persuade her to get a registered sparky in to swap the shed CU, she’s not going to swap it for anything other than a basic garage unit.
And looking at the garage units on screwfix and toolstation, most of them just have an rcd protecting 2 mcbs.
So in the event of an earth fault everything’s switching off anyway regardless if the 30ma protection is in the house or in the sheds CU.
And ild rather have it in the house as the cables twin and earth under floorboards in the house and only goes to SWA when it goes outside.
I think I’ll just use some wago connector blocks for 6mm cable and come off the supply cable to an outdoor socket. I can do all the tests to make sure rcd times are met and ZS is ok.
I don’t do Notifiable work as it’s easier to get a registered guy in, so as long as what I have planned isn’t Notifiable then I’m happy to proceed.
thanks again for all the advice
From your last post are you an electrician. Your last thread on a similar topic suggests this circuit doesn't have additional rcd protection.
Reactions: penguinlicker
Hi,
im an electrician working in the water industry. The circuit will have rcd protection as soon as it arrives from the suppliers,
OK, that sounds fine.
Email
Time zone
Last seen
Connect Sockets To Shed Supply
penguinlicker,
7029 dave,