Hi All

Taking a Zs from a light switch and am reading 160 volts between L & E.
What would you code this. I think it could be a neutral fault but I don't have the time available to investigate. The location is a hotel room.
 
Before you can Code you need to confirm the cause and effect, if you are doing EICRs this should be knowledge you possess.
 
C2 - check the earth continuity - bet there isn't any ..........
The OP should be aware of this if carrying out an EICR.
 
The OP should be aware of this if carrying out an EICR.

You will have to have a bit of patience with me as up to a year ago the only experience I had of a ring circuit was at 11000v,the last phase rotation test was on a 11000v , 7.4 MW ,slip ring motor and my last-phasing out was paralleling two 5MVA 1100/550V Dyn 11 transformers. The signing off package ran to volumes.

Having said all that I am also autherized to switch 33000V systems.

The OP was aware
 
You will have to have a bit of patience with me as up to a year ago the only experience I had of a ring circuit was at 11000v,the last phase rotation test was on a 11000v , 7.4 MW ,slip ring motor and my last-phasing out was paralleling two 5MVA 1100/550V Dyn 11 transformers. The signing off package ran to volumes.

Having said all that I am also autherized to switch 33000V systems.

The OP was aware
Don’t you go round wiring up 11kV rings anywhere near me not something I want to come across on a domestic/commercial EICR :p most of the time someone on here will assume the worst we are all guilty of it with the limited info most OPs give and the amount of chancers we get on here doing their own work and nuggets that don’t know their earth from their a**e :eek:

Edit: I’ve never heard that saying before so I’m copyrighting it and making it a trademark don’t steal it ;)
 
Other test results?

R1+R2?

IR testing?

And out of curiosity why Zs from a switch position and not furthest point of the circuit?
 
  • Agree
Reactions: Zdb
You will have to have a bit of patience with me as up to a year ago the only experience I had of a ring circuit was at 11000v,the last phase rotation test was on a 11000v , 7.4 MW ,slip ring motor and my last-phasing out was paralleling two 5MVA 1100/550V Dyn 11 transformers. The signing off package ran to volumes.

Having said all that I am also autherized to switch 33000V systems.

The OP was aware

That's lovely, but as far as I know completly irrelevant to your original question and any testing carried out to bs7671.
This suggests you have less than a years experience of working on installations at lv and to bs7671, so approximately the same experience as a first/second year apprentice.
 
  • Agree
Reactions: Blissof89 and Zdb
Hi All

Taking a Zs from a light switch and am reading 160 volts between L & E.
What would you code this. I think it could be a neutral fault but I don't have the time available to investigate. The location is a hotel room.


Not being funny, but you tested L - E, got 160v, and you think it could be a neutral fault??? How?? You were not testing for a PD across L&N? Unless of course, a PEN conductor was down, but then I would hope you would have noticed other interesting things too lol. Obvs, that last bit was a joke!

As Murdoch has already suggested, you clearly have a floating cpc/earth.
 
That's lovely, but as far as I know completly irrelevant to your original question and any testing carried out to bs7671.
This suggests you have less than a years experience of working on installations at lv and to bs7671, so approximately the same experience as a first/second year apprentice.
You obviously don't get the joke, lighten up a bit
 
You obviously don't get the joke, lighten up a bit

Do enlighten us, what is the joke?
You are carrying out an eicr, what is the joke?
Electrical safety at any voltage is far from a joke, if you have a clue you will realise electricity can, and will, kill without any regard for your opinion of whether it is funny or not.

Personally I don't care, but I'm lead to believe that the death of humans is unacceptable?

However I am curious as to how a liver and bacon casserole would taste with hunan liver? I've made it with all of the commonly available livers but humans are somewhat harder to come by for some reason? Perhaps once a few people have died from your approach to electrical safety you could cut out their livers and send them to me, I'll be happy to invite you to dinner to try this particular delicacy.
 
  • Funny
Reactions: Yplan
Other test results?

R1+R2?

IR testing?

And out of curiosity why Zs from a switch position and not furthest point of the circuit?
Perhaps the switch is the furthest point!
 
  • Agree
  • Disagree
Reactions: 2 people
Hi All

Taking a Zs from a light switch and am reading 160 volts between L & E.
What would you code this. I think it could be a neutral fault but I don't have the time available to investigate. The location is a hotel room.
Out of curiosity why are you quoting the units of zs in volts??
I thought it is measured in ohm
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Swansea
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Michael Jones Electrical Inspection

Thread Information

Title
Fault on lighting cct prevents taking Zs
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
47

Thread Tags

Advert

Thread statistics

Created
Michael J,
Last reply from
Harry_P,
Replies
47
Views
6,419

Advert