Just need some info on fire alarms panel, wiring and testing. As I am quite new to these. Why eol resistors are used.
 
eol devices are used so that the panel "sees" them in non-fault conditions. if it doesn't see the device, it goes into fault ( e.g.open circuit cable ). if it sees a resistance of , say, < 1K Ω, it goes into fire
 
All will depend on what make of panel you are using....The basic method of fire alarm panels, is to monitor the cable as well as detecting a fire condition. Making a system, able to report a fault on the cable or device. The control panel has a comparator circuit, which basically measures the voltage, in relation to the resistance (ohms law, as Tels post) so in normal operation 6k8 ohms/24v = ok.. 470 ohms/8v = fire.. 0 ohms/27v = o/c fault....>6k8 ohms/<2v = n/c fault. Hopefully diagram will help

Conventional operation.jpg
 
  • Like
Reactions: 1 person
What does the first switch in that diagram represent?
Unless I'm being daft it looks like it puts a 470r in series with a 6k8 which would raise the potential the comparator above 24V and show an open circuit fault wouldn't it?
 
  • Like
Reactions: grantrgolden
Sorry I have made a mistake in this diagram the 470 ohm resister should be switched against the blue negative line as others are show......Thanks for spotting that Dave....updated

Conventional operation.jpg
 
Last edited by a moderator:
fine if the eol is a pure resistor. some are more complex and as such can't be read on a multimeter. hoewver it's easy to operate a call-point and get the expected 470Ω .
 
Early SWL systems on cranes (pre pre CanBus) had similar arrangement for assessing conditions,three interlocks,or limit switches with varying resistor values,basic control board determined what was happening by reading resistances or combination of,O/C or full continuity reading as a separate fault. Cannot say i miss monkey clambering up a 300' strut jib with a gas soldering iron and a bag of assorted resistors...:willy_nilly:
 
fine if the eol is a pure resistor. some are more complex and as such can't be read on a multimeter. hoewver it's easy to operate a call-point and get the expected 470Ω .
The resistor is the most common method, using 470 call points, but as you stated Tel ...Active eol units are on the market, but less common now as most have been taken off the market with new EN ruling.
 
Early SWL systems on cranes (pre pre CanBus) had similar arrangement for assessing conditions,three interlocks,or limit switches with varying resistor values,basic control board determined what was happening by reading resistances or combination of,O/C or full continuity reading as a separate fault. Cannot say i miss monkey clambering up a 300' strut jib with a gas soldering iron and a bag of assorted resistors...:willy_nilly:
They were very simple but a clever idea, using binary code depending on the order of 4 switches. you could control 15 separate operations down 4 cables.....this is now the basic principle of cambus and addressable alarm systems using 8 switches to select the binary code, but now it can be sent on a 2 wire power line, with over 250 separate operations.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Fire alarms installation and testing
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
saishake,
Last reply from
tazz,
Replies
12
Views
4,024

Advert