Hi,
I have attached the findings of an IPM4 report on a house I am looking to purchase.
What I want to know is how critical are any of the points highlighted? do they pose any serious risks etc
Any help would be greatly appreciated.
Thanks,
electrical report.jpg
 
Welcome to the forum MillerDave. To answer some of the above we will need to know a couple of things. Is this a single dwelling property or part of a set of flats/apartments (#1)? What Kw ratting is the shower (#4)? What is the age of the existing wiring (#7).
 
Hi Millerdave, who commissioned the report? If it was you I'd get another one done by a competent electrician. Every observation has either 2 codes or a star, neither is accectable, and as Murdoch says there is no code 4.
 
  • Like
Reactions: 1 person
Items 5 & 7 are interesting as well?
 
Yes have to agree with others it looks like the person who filled out the report does not know how to fill it out correctly , and there in no requirement to fit cross bonding to boiler (item 5)
 
OP.

Please follow this link and take a read.....

http://www.----------------------------/mediafile/100404922/Best-Practice-Guide-4-Issue-4.pdf
 
brief look and most of it is just a tidying up of exposed connections. nowt serious there. as for the shower cable. if it's notin insulation and the shower is no more that 9.5kW, then 6mm should be fine, subject to an on site inspection.
 
  • Like
Reactions: 1 person
Sound words from Tel. Loads of people panic when they see a shower on 6mm. That's cos they can't do the calcs. Or can't be bothered. Daz
 
  • Like
Reactions: 2 people
I agree with Flanders. No requirement to fit cross bonding on the pipes at the boiler. They are usually at the same potential as they are all connected into the same conductive frame!
 
  • Like
Reactions: 2 people
brief look and most of it is just a tidying up of exposed connections. nowt serious there. as for the shower cable. if it's notin insulation and the shower is no more that 9.5kW, then 6mm should be fine, subject to an on site inspection.
Yes I was thinking that too but the observation did not explain the reason so we are only guessing why it was coded, a 6mm clip direct will take 47 amps but if its under the scratchy stuff its goes down to 27 amps (of course these figures are without any other calcs but should not change much in a domestic environment)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Help Needed on results of an IPM4 electrical report please
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
millerdave,
Last reply from
Flanders,
Replies
10
Views
1,711

Advert