I genuinely don't know how to quantify this one. It comes up fairly often on here and I've raised it before too. If it happens, it's certainly a nightmare scenario.
But stats seem to suggest we are taking around 500 occurrences in about 25 million properties in a year. So chances of any given property having this issue are mathematically miniscule. As new builds are almost all PME and more supplies are converted the number of incidents are bound to marginally increase as there are simply more out there.
Thing is, we don't tell people they might die crossing the road to go and buy the beer to have in the hot tub even though it is far more likely. Thoughts welcome!
The only time we get loss of neutral on our network in the North West is on certain type of mains cable (consac) its renown for it. The reason being that under the pvc the neutral/earth is full aluminium and as soon as water tracks in the aliminium oxidises over time and the neutral breaks down. The newer cables we install although they are cheap the neutral/earth's are split strands of copper and the odds over half of those strands corroding is very very low. In 12 years of being a jointer I have never worked on a neutral fault that didn't revolve around a consac main. We are however looking at a huge issue over the next few years with cables running above there capacity with the introduction of electric charging points and the amount of appliances in every home these days. The network is old and no one is willing to pay the money to update it. Everything is reactive maintenance in my industry not preventative.
 
But stats seem to suggest we are taking around 500 occurrences in about 25 million properties in a year. So chances of any given property having this issue are mathematically miniscule.
In my whole career, I've attended two such incidents, live (pun intended), and also found historical evidence on third place (took off a bath panel, and found a very charred 6mm G/Y running under the full length of the bath. Initially cursed wetpants and his blowlamp, but odd because the whole six foot length I could see was charred and bubbled up. Further investigation identified the wire as the bond to the water main from the MET, avoiding a few joists by passing under the bath). Only one house further up the service, so this can only have been caused by a broken neutral to next door.
 
There arent many true TN-S systems anymore. As I jointer everytime we drop a section of cable in especially within our area the cable is always PME'd in the joint. Everytime a new substation is installed or a board change is done the legs in the substation out of the new board are pme even if they are being jointed onto a split supply.

Shame as i personally feel TN-S is a much better system (despite the cost of an extra conductor)

The typical reasoning is the DNOs can no longer get TN-S cable as its not made anymore (although perhaps because the DNO stopped buying) if cable manufacturers can make 3 core copper concentric cable, i would presume they can make 4 core

I have also seen evidence of UKPN combining the E and N (PME) to repair sections of the old TN-S lead covered cable (I wonder if the tell the customers !)
 
The only time we get loss of neutral on our network in the North West is on certain type of mains cable (consac) its renown for it. The reason being that under the pvc the neutral/earth is full aluminium and as soon as water tracks in the aliminium oxidises over time and the neutral breaks down. The newer cables we install although they are cheap the neutral/earth's are split strands of copper and the odds over half of those strands corroding is very very low. In 12 years of being a jointer I have never worked on a neutral fault that didn't revolve around a consac main. We are however looking at a huge issue over the next few years with cables running above there capacity with the introduction of electric charging points and the amount of appliances in every home these days. The network is old and no one is willing to pay the money to update it. Everything is reactive maintenance in my industry not preventative.
How common are lost neutrals in your experience?

It is easy to slag of the network saying things should be better, but i bet you guys are working hard fire fighting most of the time as you say, leaving little resources left to upgrade
 
I genuinely don't know how to quantify this one. It comes up fairly often on here and I've raised it before too. If it happens, it's certainly a nightmare scenario.
But stats seem to suggest we are taking around 500 occurrences in about 25 million properties in a year. So chances of any given property having this issue are mathematically miniscule. As new builds are almost all PME and more supplies are converted the number of incidents are bound to marginally increase as there are simply more out there.
Thing is, we don't tell people they might die crossing the road to go and buy the beer to have in the hot tub even though it is far more likely. Thoughts welcome!
Likewise, very hard to put a figure on it and I wonder how many are not reported, most of the reported figures are found in publications from people selling pen protection EV products , so that does make you wonder

I suppose with a new part of the network with new concentric cable and the least amount of joints correctly done the risk is probably low, however on the other end of the scale is my windy village with seperated overhead cables with the PEN on the bottom slung over some farm entrances in which tall vehicles go in and out off

I have never has an exspirence of a PEN fault however it must be a big enough risk, otherwise why all the new regulations for EV charging and why is PME not allowed to be used in alot of situations. I wonder with more EVs and people using power outside (lockdown hot tubs) we will see a rise in PEN fault incidents

I might die crossing the road, I best stay in
 
How common are lost neutrals in your experience?

It is easy to slag of the network saying things should be better, but i bet you guys are working hard fire fighting most of the time as you say, leaving little resources left to upgrade
Not very common, the issue generally revolves around the cable I mentioned before (consac) it was a very badly designed and cheap cable that was laid from the 70's right through to the early 90's. There's cable thats been in the ground 100 years and is still in perfect condition but sections of it through other utilities and over load are starting to suffer but with that cable it tends just to blow a phase and become open circuit usually down to the lead plumbs failing and moisture tracking in
 
Shame as i personally feel TN-S is a much better system (despite the cost of an extra conductor)

The typical reasoning is the DNOs can no longer get TN-S cable as its not made anymore (although perhaps because the DNO stopped buying) if cable manufacturers can make 3 core copper concentric cable, i would presume they can make 4 core

I have also seen evidence of UKPN combining the E and N (PME) to repair sections of the old TN-S lead covered cable (I wonder if the tell the customers !)
TN-S or as us commoner cable jointers call it "split" is 100% still manufactured we actually stock it but for some reason the majority of the company will opt for its 3 core version due to it already being PME'd at the substation. Its actually easier to joint on the 4 core version than it is the 3 core so I have no idea why we do it the way we do but it's been the norm all the time I've been in the industry. As for customers or the electricians they would have absolutely no idea as to what the feed really is because if there has ever been a fault repair prior to there connection it's more than likely been combined on that section making their service pme
 
TN-S or as us commoner cable jointers call it "split" is 100% still manufactured we actually stock it but for some reason the majority of the company will opt for its 3 core version due to it already being PME'd at the substation. Its actually easier to joint on the 4 core version than it is the 3 core so I have no idea why we do it the way we do but it's been the norm all the time I've been in the industry. As for customers or the electricians they would have absolutely no idea as to what the feed really is because if there has ever been a fault repair prior to there connection it's more than likely been combined on that section making their service pme

Maybe the 3 core is cheaper, that's very interesting though, thanks for that, iv heard alot of people say the 4 core is not made, good to know it is

what is the common practice for petrol stations surrounded by PME, as far as i know PME is not allowed for petrol station forecourt, dedicated TNS supply or TT? just out of curiosity
 
Maybe the 3 core is cheaper, that's very interesting though, thanks for that, iv heard alot of people say the 4 core is not made, good to know it is

what is the common practice for petrol stations surrounded by PME, as far as i know PME is not allowed for petrol station forecourt, dedicated TNS supply or TT? just out of curiosity
Yes it will definitely be cheaper but I don't think it would be by much to be honest, the only difference between the cables is 1 less aluminium core so surely it can't add that much to the cost. As for petrol stations I've no idea, thinking back all the ones I've ever worked on through faults have been TNS supplies but whether they are true TNS I would highly doubt
 
The only time we get loss of neutral on our network in the North West is on certain type of mains cable (consac) its renown for it..... In 12 years of being a jointer I have never worked on a neutral fault that didn't revolve around a consac main.
Your insight into this area is much appreciated. I think much of the concern around TNC-S has resulted from the general lack of information within the electrical industry about it. The number of posts on this forum alone is a reflection of that.
As electricians we need to know what we are dealing with the pro, s and the con, s. To scaremonger is to do the industry and the public a disservice. To ignore the potential risks is equally wrong.
I would suggest the "crossing the road analogy" as mentioned by "Tim Howard" is the way to go. Educate people about the potential risks.
Similar to a TT system there are potential risks. It's essential that rcd, s are regularly tested to ensure safety.
 
IMO i think making a house a pme is most dangerous especially a pen fault.
Me thinks a system has a TNS is better for faults has it has a true earth not a one that being tagged to neutral, but you may think it all goes back to the grid.
You has well make all property's TT system in which you know will go earth
Ask the Spanish they been doing it for year, or any Eastern countrys are we behind or what.
 
  • Like
Reactions: marcuswareham
Your insight into this area is much appreciated. I think much of the concern around TNC-S has resulted from the general lack of information within the electrical industry about it. The number of posts on this forum alone is a reflection of that.
As electricians we need to know what we are dealing with the pro, s and the con, s. To scaremonger is to do the industry and the public a disservice. To ignore the potential risks is equally wrong.
I would suggest the "crossing
I wonder what the odds on are on this.. Im on call today and about to make my way to a loss of neutral. The funny thing is the cable feeding these property's is a a split main and not PME ?
 
wonder what the odds on are on this.. Im on call today and about to make my way to a loss of neutral. The funny thing is the cable feeding these property's is a a split main and not PME
I wonder if the the houses have got hot
Tubes in the garden, on foot in the grave. Lol
 
What an interesting thread. I think @Samhhh may have answered more questions than had answers given ?.
 
Ask the Spanish they been doing it for year, or any Eastern countrys are we behind or what.
There are trade-offs both ways. On TN systems you should be able to disconnect on the OCPD under earth fault conditions, so in that sense it is safer than relying on the RCD electronics. Of course you still want the RCD as most of the time it would disconnect on an electric shock type situation.

Down-side is the open PEN risk for outdoor equipment. In that past that was very little, probably a few floodlamps and often they are out of reach (OK, on fence another issue...)

TT avoids the issue of open PEN faults but then you need an RCD to achieve disconnection with any realistic earth rod installation. And you also have the issues of installing and maintaining rods in built up areas, etc. Of course you can reduce the impact of RCD reliability by having both a 100mA delay incomer and your usual 30mA instant "additional protection" RCDs/RCBOs so you don't have any single point of failure, but I would guess many TT installs just have the one RCD in any given circuit's path.

Any idea of how TT supplies are done in blocks of flats? Do they have a communal earth system?
 
  • Like
Reactions: marcuswareham
What an interesting thread. I think @Samhhh may have answered more questions than had answers given ?.
It has been most informative and helpful to hear the other side of the coin on this from a cable jointers perspective. I hope he continues to linger around this forum!
 
Time to bring back the old voltage operated ELCB?
That's as well as, not instead of, RCCDs
They would need to disconnect the CPC as well, much like the Zapi chargers, etc, do.

It is a solvable problem, but who should carry the cost of solving it is another matter altogether!
 
  • Like
Reactions: stevethesparks
Excuse quick diversion, then back to interesting TNS question!

In addition, one could argue that:
-GN7 says hot tubs outside should have section 702 applied.
-702.140.3.4.3 (ii) NOTE says:
"Where a PME earthing facility is used as the means of earthing [.....] it is recommended that an earth mat [...] of suitably low resistance e.g. 20 ohms or less , be installed and connected to the supplementary bonding."

Ok, I accept that's a recommendation based on a guidance note but had it been followed the (likely) problem in this thread wouldn't have happened.
Using an earth mat is a little bit different to a single earth rod
How much thought does anyone give as to where they decide to knock an earth rod into the ground, step potential under fault conditions could be interesting especially around a hot tub
The only time we get loss of neutral on our network in the North West is on certain type of mains cable (consac) its renown for it. The reason being that under the pvc the neutral/earth is full aluminium and as soon as water tracks in the aliminium oxidises over time and the neutral breaks down. The newer cables we install although they are cheap the neutral/earth's are split strands of copper and the odds over half of those strands corroding is very very low. In 12 years of being a jointer I have never worked on a neutral fault that didn't revolve around a consac main. We are however looking at a huge issue over the next few years with cables running above there capacity with the introduction of electric charging points and the amount of appliances in every home these days. The network is old and no one is willing to pay the money to update it. Everything is reactive maintenance in my industry not preventative.
Which DNO do you work for?
 
Using an earth mat is a little bit different to a single earth rod
How much thought does anyone give as to where they decide to knock an earth rod into the ground, step potential under fault conditions could be interesting especially around a hot tub
You have raised a very interesting question there. Gonna ponder that one...
 
You have raised a very interesting question there. Gonna ponder that one...
It is one of the things that sticks in my mind, about 20 years ago I was asked about putting lightning protection on a steel shelter out on a golf course I had some very interesting conversations with some very knowledgeable lightning protection people about earth rods, earth mats, voltage gradients and step potentials as the shelter was already part built and as it was too late to put an earth mat under the shelter and around it the optimum solution was do nothing as even earthing the structure could actually cause more problems than it would have solved, I realise we are talking a lot more voltage with lightning but I'm sure a low voltage high current fault could have similar consequences
 
It is one of the things that sticks in my mind, about 20 years ago I was asked about putting lightning protection on a steel shelter out on a golf course I had some very interesting conversations with some very knowledgeable lightning protection people about earth rods, earth mats, voltage gradients and step potentials as the shelter was already part built and as it was too late to put an earth mat under the shelter and around it the optimum solution was do nothing as even earthing the structure could actually cause more problems than it would have solved, I realise we are talking a lot more voltage with lightning but I'm sure a low voltage high current fault could have similar consequences
all golfers should wear lightning protection. big aerial onto top of golf cap, wired down golfing jacket to testicles.
 
whole new take on the "lost balls" situation.
 
all golfers should wear lightning protection. big aerial onto top of golf cap, wired down golfing jacket to testicles.
Some of lightning protection people did mention something about rearranging golfers balls if the step potential was to high
 
  • Like
Reactions: loz2754
Your insight into this area is much appreciated. I think much of the concern around TNC-S has resulted from the general lack of information within the electrical industry about it. The number of posts on this forum alone is a reflection of that.
As electricians we need to know what we are dealing with the pro, s and the con, s. To scaremonger is to do the industry and the public a disservice. To ignore the potential risks is equally wrong.
I would suggest the "crossing the road analogy" as mentioned by "Tim Howard" is the way to go. Educate people about the potential risks.
Similar to a TT system there are potential risks. It's essential that rcd, s are regularly tested to ensure safety.
It is one of the things that sticks in my mind, about 20 years ago I was asked about putting lightning protection on a steel shelter out on a golf course I had some very interesting conversations with some very knowledgeable lightning protection people about earth rods, earth mats, voltage gradients and step potentials as the shelter was already part built and as it was too late to put an earth mat under the shelter and around it the optimum solution was do nothing as even earthing the structure could actually cause more problems than it would have solved, I realise we are talking a lot more voltage with lightning but I'm sure a low voltage high current fault could have similar consequences

Isnt the idea that ADS reduces this risk due to rapid disconnection, and the risk could be the same from being in contact with exsposed conductive parts at the time of a fault?
 
You have raised a very interesting question there. Gonna ponder that one...
Your point about step voltage is valid. In fact it's inevitable for any earth rod/mat with a res. of 20 ohm(or1 10 ore even 5.) So while a 20 ohm earth mat would alleviate the "tingle" felt by the OP while stepping out of his hot tub, the same mat could become a serious liability under an open PEN fault. It could well be at mains potential and there would be a significant step voltage so you would not want to be in bare (and wet) feet while walking away from the tub.
So, we are back to the same issues once again with TNC-S. Yes, it's getting a bit repetitive, is, nt it!!
 
So, we are back to the same issues once again with TNC-S. Yes, it's getting a bit repetitive, is, nt it!!
Anyone fancy forming a political party called the Tea Tea Party with the sole manifesto promise of converting the entire country to TT?
 
Count me out, I'm sticking with my TNS!
May need to have a larger Tx installed in a couple of years though (possibility of two new dwellings), so who knows what I'll end up with then.
 
the same mat could become a serious liability under an open PEN fault. It could well be at mains potential and there would be a significant step voltage so you would not want to be in bare (and wet) feet while walking away from the tub.
That also depends on how deep the mat is as that impacts on the voltage gradient seen at the soil surface.
 
  • Like
Reactions: LastManOnline
You can get software to compute step & touch voltages for any sort of earthing structure, but (a) it is complex to use, and (b) it costs in the region of £5k per year or more to license (SafeGrid tell you, some others like XGSLab are a bit less forthcoming). So as you can guess it only gets used for major projects like the design of HV substation safety, etc!

It is a shame that someone with access to it did not run a few examples for typical hot tub sizes and so on to get the overall size & depth needed to ensure no more than 50V surface step even for a full 230V PEN on the buried mat.
 
to ensure no more than 50V surface step even for a full 230V PEN
Searched in "Special locations" in Irish regs regarding "hot tubs". Not a mention!!. The more you think about it, a hot tub is similar to a wet room, but with an extra layer of risk. It's a "Special, special location". We use bonding in bathrooms for protection under fault conditions. But we assume the bathroom floor is either non-conductive or not a significant factor. However with a hot tub, we stand on a surface which may be very conductive
 
It's a bit late for creative thinking and there's probably at least one flaw in this...
But would it work if hot tubs had a triple pole voltage sensitive relay on the supply held closed by it's own supply, and special dispensation to switch the earth, then in broken PEN situation hopefully the volt drop caused by higher resistance alternative path via CPC's, bonding etc. to real earth would open the relay and complete disconnection would occur?
 
It's a bit late for creative thinking and there's probably at least one flaw in this...
But would it work if hot tubs had a triple pole voltage sensitive relay on the supply held closed by it's own supply, and special dispensation to switch the earth, then in broken PEN situation hopefully the volt drop caused by higher resistance alternative path via CPC's, bonding etc. to real earth would open the relay and complete disconnection would occur?
Is this not effectively what the matt:e and similar devices do by closing a N.O 3 pole relay/contactor if the voltage is >207v & <253v. ( 722.411.4.1(iv) )

This doesn't work in a lot of situations as it is uncommon for each of the 3 phases on the DNO network to be balanced in such a way to ensure this on each phase, during a PEN fault 1 or more of the phases can remain within the voltage range but there can still be a very high voltage on the PEN conductor

Also bonded extraneous conductive parts can provide a high resistance path for the current to return, but if the load current is higher than what the bonded pipes can sink and by around the right percent it can mean that the voltage is still close to the expected 230v but you have a high voltage on the PEN conductor

If you wanted to keep the PME earth and could still sink a rod (can probably be a pretty small rod as doesn't need a low resistance) A way could be too use a voltage sensing relay measuring the voltage between the PME earth and the "test" rod, and if the voltage goes above 50v then it would open a 3 pole relay/contractor isolating L, N and PE
 
Last edited:
A way could be too use a voltage sensing relay measuring the voltage between the PME earth and the "test" rod, and if the voltage goes above 50v then it would open a 3 pole relay/contractor isolating L, N and PE
A voltage operated ELCB, as we used years ago, but breaking the supply earth as well.
 
  • Like
Reactions: LastManOnline
what was the outcome of this? I couldn't be bothered to read all 7 pages.


In America where they have more swimming pools they make more fuss about stray voltages

"In our case, stray voltage is coming from the grounded conductors of an electrical system nearby and the surrounding “earth” ground. When you are dealing with a pool, stray voltages usually feel like a small tingling sensation when you touch a puddle of water on the pool deck or a handrail/ladder attached to the pool. In the most extreme of cases, electricity in pools can cause paralysis and ultimately lead to drowning."

 
A voltage operated ELCB, as we used years ago, but breaking the supply earth as well.
I have long advocated a similar type solution. I don't understand why this option has not being explored more
 
what was the outcome of this? I couldn't be bothered to read all 7 pages.


In America where they have more swimming pools they make more fuss about stray voltages

"In our case, stray voltage is coming from the grounded conductors of an electrical system nearby and the surrounding “earth” ground. When you are dealing with a pool, stray voltages usually feel like a small tingling sensation when you touch a puddle of water on the pool deck or a handrail/ladder attached to the pool. In the most extreme of cases, electricity in pools can cause paralysis and ultimately lead to drowning."

I would suggest you read the whole thread rather ask for a synopsis

I would also suggest you read the link you posted which clearly highlights the differences between the UK and US electrical systems and the differences in test equipment used and obviously the installation tests that are carried out
 
I have long advocated a similar type solution. I don't understand why this option has not being explored more
Until EV came along in large numbers no one really bothered much about the open PEN problem.

But the flaw with the idea of opening the supply CPC is many houses will end up connected to the neighbour's PEN by virtue of bonded pipes, etc. Unless everyone on your "extraneous conductive neighbourhood" uses such a device it might well fail in practice to avoid high metalwork potentials.

Really the most practical routes are either very good additional earths, such as building foundations or a decent sized mat, or putting the tubs on a TT supply. Of the two, the local good earth is better as it ought to save you from over-voltage damage to equipment, but the TT option is likely to be easier to implement in practice.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Hot tub electric shock
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
97

Advert

Thread statistics

Created
Samhhh,
Last reply from
marcuswareham,
Replies
97
Views
15,144

Advert