I have been asked to carry out intial testing and inspection of a large, new commercial project and have came across a ring main wired in twin + cpc 1.5mm cable, which serves two 2kW panel heaters. The cables are clipped direct for part of the run and for the remainder they are within an insulated Gyproc partition wall. The protective device is a 20A type B and the cable run is 20 metres. I appreciate that it is normally 2.5mm csa cable used for this purpose, however I have looked at the 17th Edition regs and it appears that the rating of a 1.5mm twin + cpc ran in insulation (worst case) is roughly 10A. I would normally replace a circuit like this just to be on the safe side but this would mean lots of associated builderswork and costs for this new client and I would like to avoid if possible.

P=IV / I/PV
> I=P/V I=4000W/230V = 17.39A

i would appreciate your feedback guys, cheers.
 
The protective device is oversized for the cable. You could downsize it to an appropriate size - most likely a 10A, which is turn isn't that likely to hold during the winter. I think you're likely to be upgrading the cable size or running in a new circuit to one of the panel heaters.
 
Actually just reread. Are you sure its a 1.5MM ring? Seems a bit of a crazy thing to install. It's not a separate supply to each of the panel heaters?
 
Would I be better off splitting the ring circuit into two radials and having two separate 10A MCBs at the distribution board? it would be easier to split the ring as the interconnecting leg between both spur's is clipped direct on the facing of the wall.

Thanks
 
I would say it's 'almost' OK!!!
Are the heaters equidistant from the supply (ie both legs carrying 9A), if so, and nothing else can be connected to the circuit, I'd pass it but make a note on the report.

Plus, specify that nothing else should be added to this circuit.
 
Last edited by a moderator:
fig.3.4 (p 249 in the red book), shows you that a 16A type B MCB requires 23Ato break in 10,000 seconds. at 17A it's off the graph, so theoretically it will never trip at 17A
 
fig.3.4 (p 249 in the red book), shows you that a 16A type B MCB requires 23Ato break in 10,000 seconds. at 17A it's off the graph, so theoretically it will never trip at 17A

The cables running in an insulated wall would put me off fitting a 16A MCB

That said it's a ring - not had any dealings with a 1.5MM, and not sure how to go about working out the CCC of the cable in that case.
 
I think it meets the requirements of the regs, albeit a bit close to the limit.:helmet:
For parallel conductors (bit dicey here) carrying equal current then you add the CCC of the cables.
Since if it is buried in insulation as the worst case then the CCC total is 20A. This is the CPD installed; but I would note the situation on the report.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Is a 1.5mm twin + cpc ring main ok for two 2kW panel heaters??????
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
super*spark,
Last reply from
Richard Burns,
Replies
12
Views
7,352

Advert

Back
Top