Hi,what are you reading these voltages,with?
First, voltage tester when checking for dead, and then multimeter for a reading
Hi,what are you reading these voltages,with?
The neutral must be making a reference to earth at some point. Maybe binding through extraneous parts?
Isolated at main switch, 2 probe volt tester between L in and neutral bar LEDs on tester 240v. I am only getting the voltage with circuits connected. As has been suggested already is one circuit the issue and giving me return path, however if I disconnect all circuits in the property then probe L in to any disconnected neutral I am also getting between 120v and 240v ( with the cpcs disconnected as well of course)So,you confirmed isolated and safe,then placed the multimeter probes at the same point,and this is the reading we are discussing?