Discuss Nuissance tripping on a 30mA Main RCD on a TT system in the Australia area at ElectriciansForums.net

I have checked the continuity of the ring main and all is well. i have isolated all the circuits and switched back on and it doesnt trip. It is tripping with randomly circuits and not a particular circuit unfortunatly.

The RCD is tripping on half load with other circuits connected.
i will test the Rcd without any outgoing connections and see if it still trips on half load.

I will have to see if i can borrow a meter with ramp testing, mine is a old robin that doesnt have the ramp test function.

Can i use a current clamp and modify a extension lead so the earth is accessible and connect the ext lead to socket then connect my device to the ext, put my current clamp on the earth and measure the current leakage when the device is on. will this be ok?
 
I have checked the continuity of the ring main and all is well. i have isolated all the circuits and switched back on and it doesnt trip. It is tripping with randomly circuits and not a particular circuit unfortunatly.

The RCD is tripping on half load with other circuits connected.
i will test the Rcd without any outgoing connections and see if it still trips on half load.

I will have to see if i can borrow a meter with ramp testing, mine is a old robin that doesnt have the ramp test function.

Can i use a current clamp and modify a extension lead so the earth is accessible and connect the ext lead to socket then connect my device to the ext, put my current clamp on the earth and measure the current leakage when the device is on. will this be ok?


Not with a conventional current clamp meter, you need a leakage amp clamp that will have a microhm resolution. Also a lot of MFT kit do not ramp in 1mA steps, but in maybe 2 or 3 mA so not a very accurate method of testing leakage trip levels.
 
If you can't locate one issue, which is very likely, I'd be talking to the client about a new dual RCD board or if the house is old, a board with a full set of RCBO's

Having one 30Ma RCD up front is a very undesirable situation for any household!
 

Reply to Nuissance tripping on a 30mA Main RCD on a TT system in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock