Hi Guys,

Got to do a periodic inspection report, there two consumer units one i cant access due to kitchen units in the way i can see the breakers but i wont be able to take the cover off and the other consumer is fine to get to.

Any Ideas what to do for the consumer unit i cant get to? or what to write on the report?

Thanks
 
All you can do is verify the circuits and give Zs and rcd readings if applicable. On the schedule of tests you can only complete the parts you know, the rest can only be NV. You can only do what you can and decide how you are going to Code it in the Report.
 
Discuss it with the customer because if they are doing it for a house sale that could become a real issue. Is there no way they can't make access to it.
 
hum..... so 50% of the installation not really in a position to test, is it worth doing?

And what code for inaccessible CU? C2?
 
  • Like
Reactions: richy3333
hum..... so 50% of the installation not really in a position to test, is it worth doing?
I think so most stuff is picked up from the visual, but yes 50% of testing won't be done but that is out of his hands.
 
I think so most stuff is picked up from the visual, but yes 50% of testing won't be done but that is out of his hands.

I would be tempted to C2 the inaccessible CU ...... that would depend on the estimated age of the installation, and whether there have been changes made!
 
Inaccessible cu not even able to open the cover, thats a C2 if there ever was!
 
I think so most stuff is picked up from the visual, but yes 50% of testing won't be done but that is out of his hands.

Isn't this where you insert in to the EICR your legendary FI quote :)
 
  • Like
Reactions: Risteard
Theres a whole estate near me approximately 100 houses with this problem . Every mains change has to coincide with a new kitchen .
 
  • Like
Reactions: DPG
hum..... so 50% of the installation not really in a position to test, is it worth doing?

And what code for inaccessible CU? C2?

Inaccessible cu not even able to open the cover, thats a C2 if there ever was!

I would instantly think C2 as well but then I thought what would I say if I was asked to justify that with regards to it being 'potentially dangerous'?
The CU and all circuits may be in excellent condition. Perhaps a 'limitation' with a strong recommendation it is made accessible for testing?
Or perhaps a C2 because it is potentially dangerous as electrical installations should be tested every 10 years and this one can not be?
 
  • Like
Reactions: Silly Sausage
He has no choice but to enter a Limitation, with a further recommendation access is enabled so a full inspection/test can be carried out.
 
I would instantly think C2 as well but then I thought what would I say if I was asked to justify that with regards to it being 'potentially dangerous'?
The CU and all circuits may be in excellent condition. Perhaps a 'limitation' with a strong recommendation it is made accessible for testing?
Or perhaps a C2 because it is potentially dangerous as electrical installations should be tested every 10 years and this one can not be?
It would also so be classed as a maintainable accessory, which means access is required for maintenances purposes, i.e checking connections etc..
 
  • Like
Reactions: Rpa07
You'd have to gain access to it to ascertain whether the CU has the MF stamp on the inside - after all it is inaccessible so needs to be maintenance free! (Where's the emoji for tongue in cheek!)
 
  • Like
Reactions: Wilko and ruston
You'd have to gain access to it to ascertain whether the CU has the MF stamp on the inside - after all it is inaccessible so needs to be maintenance free! (Where's the emoji for tongue in cheek!)
Actually you make a valid point. :)
 
  • Like
Reactions: Rpa07
How on earth can you test the install if the cu is inaccessible? You cant even do basic testing or check terminal tightness, visual, polarity, main isolation. It isnt FI its a unstaisfacory, and if any sparks agreed in the lims not too take cover off cu then he needs reporting to his scheme imo. C2 no doubt!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
periodic inspection report no access to the consumer unit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
sparky928,
Last reply from
unconditional,
Replies
22
Views
3,340

Advert