Ian Pankhurst

I'm a little confused as I have been off work for a while and not had that much electrical work on recently and am a bit of a noob if I'm honest.
The issue is that the rcd was tripping with all the breakers off. I took out the buzzbar next just to make sure. With the main breaker on the rcd still wouldn't stay on. So I changed the rcd and still the same, do I then changed the main switch and, you guessed it, still the rcd won't stay on?!?!
there is absolutely nothing on the system, only main feed in.
What tests do I have to do to find the fault or does anyone know what on earth it could be?
 
What tests have you actually carried out?
What test equipment do you have?
Have you carried any work on the installation that may cause this to happen ( please be honest or we don't stand a chance of helping you) C
 
Have you disconnected all the live conductors connected to the RCD? Then tried switching it on?
 
hint... N-E.
 
you possibly have a neutral to earth fault , if you had a lot of rain last night then check the outside lights for water , and get test kit out , you'll need to check each circuit disconnect each circuit from the neutral bar and MCB in turn and test them or with all the MCB's switched off disconnect each neutral till the fault clears and then test the circuit that causes the fault much prefer the dead testing method
 
  • Like
Reactions: 1 person
In Feb 2013 you were buying a Megger MTF have you not being using it ? post a picture of the CU
or a bit more info. in your op you say what on Earth could it be...thats a good clue
 
Tails from the meter go to the main switch, switch to rcd, rcd to nothing, as I have taken out the buzzbar. I just disconnected the neutral from the rcd to the neutral bar in the CU and the rcd stained on, so maybe a neutral fault?
 
Think we all said that its tester out and test between neutral and earth on each of the neutrals till you find the fault
 
  • Like
Reactions: 1 person
then connect each circuit 1 at a time, switching on the RCD. then you've tracked it to the faulty circuit.
 
  • Like
Reactions: 1 person
7 minutes since someone suggested the test to you have you had time to IR test all the circuits ? just asking

What's it test is fine mean?
 
  • Like
Reactions: 1 person
All sorted, thanks for pointing me in the right direction and jogging the memory again lol
it was a dodgy spur off the upstairs ring main. It wasn't needed anymore, so removed it and it's all back to normal now. Cheers boys
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Rcd keeps tripping out
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
Ian Pankhurst,
Last reply from
nults,
Replies
33
Views
3,970

Advert