Ooh, using a wander lead I got a reading form the CU L to the dimmer L/com, and the L on the ceiling rose was removed...?!
 
What else has your customer replaced, possibly a socket also. As its been said you need to IR test, and all common shared neutrals on that side of the rcd.
 
Like the other guys have said you need to do IR test, if the readings are bad then go looking for damaged or faulty cables, then you can narrow it down by doing IR tests on separate parts of the circuit
 
I know it sounds harsh, but you need to stop jumping around trying to find a fault, you need to start testing correctly and not jumping between test procedures, you will spend all day chasing you tail if you carry on the way your are "testing"
 

Reply to RCD tripping even with all switches and bulbs removed. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
453
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
577
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
795

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock