Motty
Gents, your opinion please.
I am still finding my feet with commercial installation principles but this is ringing alarm bells ...
My customer wants a small DB for 6 single phase AC units to be fed from the last spare 3pole MCB in a 12way DB - " a sub-sub main" for want of a better description. He owns a small-medium sized AC installation firm who I am starting to to do sub-contracting for.
This would be fed by taking 3 x 10mm2 lines from a C-63A MCB to a small 6-way board with the loads split across the 3 phases; with neutral and earth connection back to the existing board. the units are 1x 3Kw, 3x 2.2kw and 2 x 1.5kw, total load of 12.6Kw, (approx 4.5 Kw per phase) total load of 52A, and the AC units being fed from C-16A and 10A MCBs.
My main concern, besides the hap-hazard arrangement, is having 2 MCBs connected in series e.g. nuisance tripping, and the neutral remaining connected to the source as and when the feed / 3phase MCB is turned off. A means of overcoming this is a 4-pole isolator connected between the boards, however this relies on the operator operating both the isolator and 3 ph MCB rather than just the 3ph MCB on its own. I think this is a bit gash tbh.
Also, the demand on the new board will be close to its 63A feed limit, and with a load of spare ways means anyone installing equipment in the future might overload it unintentionally. And labelling it with "do not connect further / additional equipment" just won't cut it imho.
Having looked at the job yesterday it would be straightforward to feed a new DB sub-main from the 11kvA transformer in the corner of the building, however this will quadruple+ the cost as its a 25 metre run to the new board position. There are 3 spare 400v ways in the switchgear cabinet, and existing cable ladder leading pretty much directly to the new board location.
your opinions, however fierce, would be appreciated. I am already thinking " we need to put a new sub main in; £**** this is what it costs, if you don't like it find another spark"
thanks in advance.
I am still finding my feet with commercial installation principles but this is ringing alarm bells ...
My customer wants a small DB for 6 single phase AC units to be fed from the last spare 3pole MCB in a 12way DB - " a sub-sub main" for want of a better description. He owns a small-medium sized AC installation firm who I am starting to to do sub-contracting for.
This would be fed by taking 3 x 10mm2 lines from a C-63A MCB to a small 6-way board with the loads split across the 3 phases; with neutral and earth connection back to the existing board. the units are 1x 3Kw, 3x 2.2kw and 2 x 1.5kw, total load of 12.6Kw, (approx 4.5 Kw per phase) total load of 52A, and the AC units being fed from C-16A and 10A MCBs.
My main concern, besides the hap-hazard arrangement, is having 2 MCBs connected in series e.g. nuisance tripping, and the neutral remaining connected to the source as and when the feed / 3phase MCB is turned off. A means of overcoming this is a 4-pole isolator connected between the boards, however this relies on the operator operating both the isolator and 3 ph MCB rather than just the 3ph MCB on its own. I think this is a bit gash tbh.
Also, the demand on the new board will be close to its 63A feed limit, and with a load of spare ways means anyone installing equipment in the future might overload it unintentionally. And labelling it with "do not connect further / additional equipment" just won't cut it imho.
Having looked at the job yesterday it would be straightforward to feed a new DB sub-main from the 11kvA transformer in the corner of the building, however this will quadruple+ the cost as its a 25 metre run to the new board position. There are 3 spare 400v ways in the switchgear cabinet, and existing cable ladder leading pretty much directly to the new board location.
your opinions, however fierce, would be appreciated. I am already thinking " we need to put a new sub main in; £**** this is what it costs, if you don't like it find another spark"
thanks in advance.