We are building a small house at a lake that has a 200 amp feed through panel at the meter pole at the street. We would like to install an underground feed to a 150 amp indoor panel at the house. Electricians want to run an SE 2/0 wire. I would prefer to run a 2/0SER RHH,RHW-2.
I believe that would give us a fire rated cable where it enters the house. I believe SE is not rated for burial. Any thoughts or recommendations?
Also, if the 150 amp panel is considered a sub panel, would I need a four conductor wire? A separate ground should be installed at the house.
 
We are building a small house at a lake that has a 200 amp feed through panel at the meter pole at the street. We would like to install an underground feed to a 150 amp indoor panel at the house. Electricians want to run an SE 2/0 wire. I would prefer to run a 2/0SER RHH,RHW-2.
I believe that would give us a fire rated cable where it enters the house. I believe SE is not rated for burial. Any thoughts or recommendations?
Also, if the 150 amp panel is considered a sub panel, would I need a four conductor wire? A separate ground should be installed at the house.
Hi and welcome to the forum and I looked up SE cable is not approved for underground with or without a raceway. If you want a subpanel yes you would have to use 4 wire cable or singles. It sounds like it will be installed underground but in your best interest your electricians need to install 2 inch PVC conduit with THHN insulation. They will need to pull two 2/0 for power and 1/0 for the neutral plus one # 6 ground wire. Any sub-fed panel has to keep the neutral wires and the ground wires separate which means they will have to have a ground bar in the panel and one bar for the neutral. Do not install a ground rod, at your main panel that the power company supplies. All the bonding takes place at the first panel using 2 ground rods I don’t recommend using RHH or RHW 2 use THHN Home Depot and Lowe’s sells THHN and not RHH or RHW 2. Good luck my friend
 
Thanks for input. Since there is a panel at the street and the panel in the house is a subpanel, wouldn’t We just pull three conductors and drive a separate ground rod at the house? Also leave the green screw off in the subpanel?
 
Thanks for input. Since there is a panel at the street and the panel in the house is a subpanel, wouldn’t We just pull three conductors and drive a separate ground rod at the house? Also leave the green screw off in the subpanel?
Yes don’t add the green screw. Your telling that the main panel is on a pole and how far is that from your home. Also walk out to the panel on the pole and see if there’s one or possibly 2 ground rods If so the new panel will be the sub- fed panel and you have to pull 4 wires as per the NEC and do not add it a rod it is a code violation. You will also as I stated before keep neutrals and grounds separate
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Underground feed
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Six character,
Last reply from
Megawatt,
Replies
3
Views
1,192

Advert

About us

  • Electricians Forums™ is a Recognised (unregistered) Trademark in the UK owned by Untold Media® which IS a Registered Trademark in the UK. We use the Trademark under licence and pay an annual fee of 250,000 GBP for it. Anybody found using the mark is liable to pay for the licence of it, and the legal costs, and court costs. We are aware of a Welsh company using the mark without permission and have activated Defensive Measure (legal route), and Offensive Measures (many that will damage their forum long-term) to take the website down via a number of routes, and to de-rank it in Google who are on our side in this case. CloudFlare is next, then XenForo who host it. Then Nominet. Then we should be able to take over the domain and shut the forum down.

Quick Navigation

User Menu