Discuss Underground feed in the UK Electrical Forum area at ElectriciansForums.net
We are building a small house at a lake that has a 200 amp feed through panel at the meter pole at the street. We would like to install an underground feed to a 150 amp indoor panel at the house. Electricians want to run an SE 2/0 wire. I would prefer to run a 2/0SER RHH,RHW-2.
I believe that would give us a fire rated cable where it enters the house. I believe SE is not rated for burial. Any thoughts or recommendations?
Also, if the 150 amp panel is considered a sub panel, would I need a four conductor wire? A separate ground should be installed at the house.
Hi and welcome to the forum and I looked up SE cable is not approved for underground with or without a raceway. If you want a subpanel yes you would have to use 4 wire cable or singles. It sounds like it will be installed underground but in your best interest your electricians need to install 2 inch PVC conduit with THHN insulation. They will need to pull two 2/0 for power and 1/0 for the neutral plus one # 6 ground wire. Any sub-fed panel has to keep the neutral wires and the ground wires separate which means they will have to have a ground bar in the panel and one bar for the neutral. Do not install a ground rod, at your main panel that the power company supplies. All the bonding takes place at the first panel using 2 ground rods I don’t recommend using RHH or RHW 2 use THHN Home Depot and Lowe’s sells THHN and not RHH or RHW 2. Good luck my friend
Thanks for input. Since there is a panel at the street and the panel in the house is a subpanel, wouldn’t We just pull three conductors and drive a separate ground rod at the house? Also leave the green screw off in the subpanel?
Yes don’t add the green screw. Your telling that the main panel is on a pole and how far is that from your home. Also walk out to the panel on the pole and see if there’s one or possibly 2 ground rods If so the new panel will be the sub- fed panel and you have to pull 4 wires as per the NEC and do not add it a rod it is a code violation. You will also as I stated before keep neutrals and grounds separate
Reply to Underground feed in the UK Electrical Forum area at ElectriciansForums.net
I am working on a RV Park and I have a question. I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and...
I am adding a 60 AMP subpanel for a detached garage/workshop with a 200 foot underground conduit run from the main panel to the sub panel...
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
The seller is saying they will not upgrade the electric and it is normal to have 100 amps. However the inspector is stating it may trip often and...
I have an outbuilding a fair distance from the house. In this outbuilding I just want to have some lights, a small music radio/clock, and a...