1000008386.jpg
 
Your profile shows you are a trainee if you are unsure of safe isolation procedures someone should be helping you.
 
As above, proving unit at the top (in pic below), voltage indicator/dead tester at the bottom.
You are presumably using a tester, and not a proving unit, to measure with 🤔
IMG_0710.jpeg
Terminology, particularly in regard to equipment and units of measurement, is important in this business!
 
As above, proving unit at the top (in pic below), voltage indicator/dead tester at the bottom.
You are presumably using a tester, and not a proving unit, to measure with 🤔
View attachment 117854
Terminology, particularly in regard to equipment and units of measurement, is important in this business!
Thanks Avo , Would be using proving unit as it is only to check no power is at the contactor before replacing it. I was just curious if the checks would be across L1-T1 and then L1-Earth as there is no neutral and it's only single phase. Also prob check there is no 24v on A1 . ? Is that correct? Thanks
 
Sorry I'm not being clear - I'm concerned with your use of the term "proving unit" in your question!
You can't use a 'proving unit' to test with!
For a start it doesn't have any probes. Its sole purpose is as a voltage source to check that a tester (another instrument) actually works.

I imagine you intend to use a tester (NOT a "proving unit') with probes (something like my lower picture) to do the checking with, first applying the probes to the proving unit to ensure the tester is working, and then in your case between a ground (which you know is actually a solid connected ground), and the terminal you want to check is dead or alive.

L1 and T1 are the connections to one 'switch' of the contactor. If the contactor is open, there may be incoming power, but not outgoing. It wouldn't be my choice to measure between them if you want to check for power.
Your other suggestion seemed more appropriate.

The principle is surely to check there's no hazardous voltage on any wires you might come in contact with. The whole thing needs to be dead!

PS I think A1 would only be 12V DC when the system is powered - a mains voltage tester might not indicate that low a voltage.
 
Last edited:
Sorry I'm not being clear - I'm concerned with your use of the term "proving unit" in your question!
You can't use a 'proving unit' to test with!
For a start it doesn't have any probes. Its sole purpose is as a voltage source to check that a tester (another instrument) actually works.

I imagine you intend to use a tester (NOT a "proving unit') with probes (something like my lower picture) to do the checking with, first applying the probes to the proving unit to ensure the tester is working, and then in your case between a ground (which you know is actually a solid connected ground), and the terminal you want to check is dead or alive.

L1 and T1 are the connections to one 'switch' of the contactor. If the contactor is open, there may be incoming power, but not outgoing. It wouldn't be my choice to measure between them if you want to check for power.
Your other suggestion seemed more appropriate.

The principle is surely to check there's no hazardous voltage on any wires you might come in contact with. The whole thing needs to be dead!

PS I think A1 would only be 12V DC when the system is powered - a mains voltage tester might not indicate that low a voltage.
Thanks I appreciate your reply. Yes I mean a tester. Thanks for the information
 
A “proving unit” simply proves your tester is working….

The procedure is, test the tester on the proving unit first (should light up) then test the wires…
Finally test on the proving unit again.

It basically proves your tester has worked throughout the sequence.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Using a proving unit to check for dead before removing this contactor. What do I probe on to ? Can someone please describe the tests i.e L1 -Earth.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
3phase,
Last reply from
littlespark,
Replies
8
Views
610

Advert

Back
Top