Hi,

Am running a radial power circuit in 4mm fp200 with a 20A rcbo but am a bit worried about the voltage drop. I have a 70M run clipped direct and by my calculations I will need to go to 6mm. I am using table 4d2 but don't know if there is a table for fp200.
 
What is your design current for the circuit?
 
As above... why FP200 as its not a common choice other than EM lighting and Fire Systems ...and what design current
 
you could perhaps use 4 core 2.5mm and parallel the conductors.
 
Just googled a manufacture they are giving a mv/a/m of 11 which is the value I used so will have to rethink or go to 6mm.
 
Find out the BS number of fp200, there's a section in the regs which will give you the correct table.
 
you could perhaps use 4 core 2.5mm and parallel the conductors.

What about Zs on this Tel...:omg_smile: might work on short run but at 70m you will have earth serving doubled up L/N, this would worry me about it meeting Zs permitted values and not a route I'd want to take...
 
Just googled a manufacture they are giving a mv/a/m of 11 which is the value I used so will have to rethink or go to 6mm.

A manufacturer? Do you mean the manufacturer? There is only prysmian who manufacture FP200 since FP is their brand name!
 
Find out the BS number of fp200, there's a section in the regs which will give you the correct table.

As FP200 is a specific product from a specific manufacturer (prysmian) there won't be a table in the regs for it, the data sheet will be the place to look.
 
Jamie - can I enquire as to the nature of the circuit, seems a strange design current given the nature of its common uses, don't get me wrong not saying your using the wrong cable just curious thats all.
 
What about Zs on this Tel...:omg_smile: might work on short run but at 70m you will have earth serving doubled up L/N, this would worry me about it meeting Zs permitted values and not a route I'd want to take...

oops. i didn't think that one out :ack2::ack2:
 
  • Like
Reactions: 1 person
Find out the BS number of fp200, there's a section in the regs which will give you the correct table.

It's BS7629-1. Table 4A3 in BGB states to use 'Applicable Current Rating Table' 4D2.
So I assume Jamie can use 4D2B for his calcs.
 
A couple of points to consider,

what is the likely loading on these S/Os ? in other words could you drop the Ib to say 16A ?

What about either making it two radials at the MCB or making it a ring ?

I am not sure if any of the above helps as obviously I don't know the layout, there are no problems, only solutions you have not thought of yet :)
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Voltage drop for fp200
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
Jamie Smith,
Last reply from
spark 68,
Replies
17
Views
9,523

Advert