Done an install a couple of years back in a large building with three large sub switchrooms fed from a common main switchroom.
All lighting throughout the installation is either hf fluorescent or pl. As I say this was installed around 2 years ago with only the odd lamp failure as would be expected.
Recently lamps have been failing more or less daily and the client got us to relamp all fittings around 4 weeks ago which has been done.
On a daily basis there are numerous lamps failing so I called in today to investigate.
First thing I noticed was most of the lamps that are still lit have blackened ends so I tested the voltage at random fittings and the highest voltage I measured was 218V. Checked a couple of the local DB's and again voltage was around 218 - 219V L-N.
Got into the sub switchrooms and noticed that voltage optimisers have been installed that have been set to 380V L-L.
I'm reckoning that these voltage optimisers are causing the lamp failures. Any opinions welcomed.
 
Not sure if PL are HF as well, probably are now but maybe not when installed, for HF I have forgotten how they operate but for ss Blackened ends means the heaters are running for a long time, perhaps there is not enough voltage at times to cause the lamp to strike, so the heaters stay on as the lamp attempts to function. However I would have thought they would be experiencing delays in lamp lighting which would have been mentioned (perhaps).
Then with the heaters on for so long they are evaporating and then failing totally.
I will think more!
 
Thanks Richard for your reply. There is a delay on quite a few fittings especially the ones with the combined emergency back up. The pl fittings are also high freq. I am trying to get something concrete on this to throw back at the client.
 
voltage optimisers wont save any power with HF ltg anyway, nor with much electronic equipment like PCs nor with A/c plant with Variable speed drives such as most modular kit has these days.... I'm struggling to think what might be left. Id set the optimiser up to 400V which is where it should be and see if the problem goes away.
 
380/220V seems far to low unless they have specialist machines. The only time I’ve come across it was on German and Belgian printing presses and bag making machines. The manufacturer refused to guarantee them at any higher voltage, all the lighting and ancillary equipment was 433/250V.

It was a crazy set up with two 1000KVA transformers at different voltages.

How difficult would it be to up the voltage to say 400/230V for a trial period?
 
On the ones we have installed. Changing the optimised output was fairly straightforward, you just needed to alter 3 jumper leads across the top of the unit. However we have only worked with one brand of unit and they probably are likely to differ.
 
On the ones we have installed. Changing the optimised output was fairly straightforward, you just needed to alter 3 jumper leads across the top of the unit. However we have only worked with one brand of unit and they probably are likely to differ.

So it would involve a shutdown to alter the jumpers. Pity!

I tried lowering the supply to our plants over several weekends by altering the 33/11KV onload tap changers.
It was a disaster.
Monday morning I was wiping my backside about 6” down from my neck. I don’t mind getting my backside kicked if it’s my fault! It was the bloody accountant that asked the senior engineer about it, we could save money. Senior engineer collard me as I was on shift most weekends, SE then cleared off on holiday and left me as guest of honour at the arse kicking party!
 
So it would involve a shutdown to alter the jumpers. Pity!

I tried lowering the supply to our plants over several weekends by altering the 33/11KV onload tap changers.
It was a disaster.
Monday morning I was wiping my backside about 6” down from my neck. I don’t mind getting my backside kicked if it’s my fault! It was the bloody accountant that asked the senior engineer about it, we could save money. Senior engineer collard me as I was on shift most weekends, SE then cleared off on holiday and left me as guest of honour at the arse kicking party!
i remember you telling me about this event tony...

and how stuff all around the plant started arsin about...lol...
 
I will be back onsite tomorrow and will have access to all the switch rooms. Will have a closer look at the optimisers and maybe get a few pictures of them.
 
So it would involve a shutdown to alter the jumpers. Pity!

I tried lowering the supply to our plants over several weekends by altering the 33/11KV onload tap changers.
It was a disaster.
Monday morning I was wiping my backside about 6” down from my neck. I don’t mind getting my backside kicked if it’s my fault! It was the bloody accountant that asked the senior engineer about it, we could save money. Senior engineer collard me as I was on shift most weekends, SE then cleared off on holiday and left me as guest of honour at the arse kicking party!

Yes, sorry, haha if it is the same type I'm talking about then the procedure is straightforward, the shutdown & effects etc may not be so!
 

Reply to Voltage optimisers and lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
769
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
We are currently renovating an old house after recently moving in. Whilst purchasing the property we received written assurances that the original...
Replies
47
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock