Alright,
im currently testing a store and come across a situation I'm a little unsure on. I've got 3 4c SWAs feeding 3 different boards, no separate earths with any of them and no fly leads from banjos to the DB their feeding or supplied from, there relying on the trunking and chassis of the main panel to get their earth, zs fine etc, so would this be a c2 or a c3 in ur opinion
im currently testing a store and come across a situation I'm a little unsure on. I've got 3 4c SWAs feeding 3 different boards, no separate earths with any of them and no fly leads from banjos to the DB their feeding or supplied from, there relying on the trunking and chassis of the main panel to get their earth, zs fine etc, so would this be a c2 or a c3 in ur opinion