im currently testing a store and come across a situation I'm a little unsure on. I've got 3 4c SWAs feeding 3 different boards, no separate earths with any of them and no fly leads from banjos to the DB their feeding or supplied from, there relying on the trunking and chassis of the main panel to get their earth, zs fine etc, so would this be a c2 or a c3 in ur opinion
Difficult one I would say C2 No I'll edit that and say C3 improvement recommended
I would say C3 as well, although I am not sure which reg would back me up on that.
If your ZDB readings are within the limits, by fitting a link from the banjo to the earthing bar should improve the readings, not got my 7671 handy so can't help with a reg noView attachment Best-Practice-Guide-2.pdf think Ive got the right one attached sorry wrong one, try looking at the best practice guide for EICRs on google cant seem to get my copy to attach
Reply to C2 or c3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I’ve just done an EICR on an old 2 bed flat that is wired in all metal conduit wired in singles however there are no CPC’s. The conduits are all...
Bit of advice please. Not too used to this stuff. In large old building, a couple of MICC radial circuits feeding a few sockets each. All tests...
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
6K
Hello, I'm after some coding advice / opinions regarding EICR of warehouses / offices. In others opinion would this be agreeable (helplines closed...