A circuit with a 10mm 70*C thermoplastic copper live conductor has a maximum final temperature of 160*C. If a fault current of 600A flows through the conductor, the time taken to reach the final temperature would be.... ? got all the rest just cant seem to locate this one! cheers in advance.:)
 
A circuit with a 10mm 70*C thermoplastic copper live conductor has a maximum final temperature of 160*C. If a fault current of 600A flows through the conductor, the time taken to reach the final temperature would be.... ? got all the rest just cant seem to locate this one! cheers in advance.:)
Check out 434.5.2
 
I asked this question as i don't really look at the regulations too much as the technical guys in the office do the groundwork for installations and such. Obviously I'm familiar with the do's and don'ts but the more in-depth stuff, well its been a while but i have enjoyed it and I'm going to keep up to date with this one lol. Oh by the way there has been minor changes already they haven't been released yet but an amendment is definitely on the horizon.​
 
k is either 115 or 143, depending if its single core cable or multicore. 160 is the temp.

143 is k value for thermosetting, 115 for thermoplastic, therefore answer is 3.67
As it is computerised, you have to be spot on with the answer, an assessor may have accepted 3.6 or 3.7 but I was marked incorrect on a computerised test paper for doing just that, rounding to nearest decimal point when the answer should have been to nearest 2 decimal points.
 
Sorry, 143 is also the value for thermoplastic single core cables.

My copy of the 18th (Table 43.1) only shows 1 figure for copper conductors, final temperature of 160deg C as k=115, for 70 deg C thermoplastic cables depending upon if less than 300sq mm.

Whether single or multicore cables, doesn't seem to have a bearing on the k figure (as far as the 18th and table 43.1 goes).

Either way 143 gives and answer (5.68s) which is obviously incorrect as it wasn't one of the multiple choice answers provided.
Another clue that it is incorrect! table 43.1 is for disconnection times upto 5seconds.
 

Reply to Can't seem to find the answer, 18th edition tommorow ; ) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net