A circuit with a 10mm 70*C thermoplastic copper live conductor has a maximum final temperature of 160*C. If a fault current of 600A flows through the conductor, the time taken to reach the final temperature would be.... ? got all the rest just cant seem to locate this one! cheers in advance.:)
Check out 434.5.2
I asked this question as i don't really look at the regulations too much as the technical guys in the office do the groundwork for installations and such. Obviously I'm familiar with the do's and don'ts but the more in-depth stuff, well its been a while but i have enjoyed it and I'm going to keep up to date with this one lol. Oh by the way there has been minor changes already they haven't been released yet but an amendment is definitely on the horizon.​
k is either 115 or 143, depending if its single core cable or multicore. 160 is the temp.
143 is k value for thermosetting, 115 for thermoplastic, therefore answer is 3.67
As it is computerised, you have to be spot on with the answer, an assessor may have accepted 3.6 or 3.7 but I was marked incorrect on a computerised test paper for doing just that, rounding to nearest decimal point when the answer should have been to nearest 2 decimal points.
Sorry, 143 is also the value for thermoplastic single core cables.
My copy of the 18th (Table 43.1) only shows 1 figure for copper conductors, final temperature of 160deg C as k=115, for 70 deg C thermoplastic cables depending upon if less than 300sq mm.
Whether single or multicore cables, doesn't seem to have a bearing on the k figure (as far as the 18th and table 43.1 goes).
Either way 143 gives and answer (5.68s) which is obviously incorrect as it wasn't one of the multiple choice answers provided.
Another clue that it is incorrect! table 43.1 is for disconnection times upto 5seconds.
Hi Stephen
can you please advise me where to obtain a revision paper for the 18th edition please?
Thanks in advance.
There's an 18th Edition 'exam simulator' here if you want a practice run.
18th Edition Exam Simulator | -----------.co.uk - http://www.-----------.co.uk/18thedition/18th-edition-exam-simulator.php
But they are for protective conductors only, not for a 'Live' conductor as per the question.
Yes, thing is, they both relate to fault current.
You would not normally size live conductors according to fault current, you’d size them according to the tables in Appendix 4, for Current Carrying Capacity, which would require a larger CSA.
Agree with some of what you say but it isn't relevant to the OP's original question!
Not so sure about that! All I think WE'VE done is confuse the OP, what with more than one member on here suggesting k=143 is the correct value to use in his question!
143 would be for single conductors.
115 is for conductors that are part of a cable.
For some reason Table 43.1, doesn’t make such a distinction?
Don’t think anyone has suggested that 143 is the correct value to use?
Changed your tune!
As you rightly said k=143 is used from table 54.2 as a single conductor but only for protective conductors, not a live conductor which was the subject of the question!
Changed your tune!
Not changed any tune.
Live conductors and CPCs both have to carry fault currents.
There’s no difference to the thermal constraints placed on them just because the insulation colours are different.
I have at no time suggested the value of k should be 143.
What I have said, is the value of k for single core cables is 143 and that the tables 54.2 through to 54.5 can be used for both live conductors and protective conductors.
We had already established that the value for k to be used in the question was 115, before you posted.
I'm sorry, I believe you are wrong tables 54.2 - 54.5 clearly state - Values of k for 'protective conductor' in the relevant heading for whatever form it may take, conduit, trunking, armour etc.
I do not believe the tables should be used for 'live' conductors, which is why table 43.1 is in the book.
I'm surprised no one else has waded in with their two penny worth!
I think we can agree to disagree on this one!
Reply to Can't seem to find the answer, 18th edition tommorow ; ) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
M
Sketch the appropriate BS EN 60617 locationsymbol i) Switched socket outlet ii) Lighting outlet iii) Distribution Board iv) Two way switched...
Hi guys, I wonder if someone would be kind enough to help me understand the answer to this question from a well known guide-book on 'Inspection...
Z
Dear Friends I have booked my 2391 exam on October 18th for third time and this is my last chance to pass it. I have about five past exam...
15K
S
I will post the answers on here in a few day or if you really want to know PM me and i will send them. Example Questions for 2382-10 1. The...
sxsparky
S