Let me explain what we're seeing here.

This is an enclosure mounted on a post near the driveway. The source wire coming up from the black pipe is fed from a 30amp double pole breaker in the house panel. Not sure if the white wire coming from the house is neutral or ground. The wire does appear to be 10/2 at least. The run is probably about 70 feet long.

I've not figured out yet where the wires in from the pipe on the right go yet. I believe they went to the nearby shed, but can't locate them in there.

Problem 1: The red wire, I guess, wasn't long enough, so they extended it with a piece of 14awg!
Problem 2: The 14/2 romex (the loose side was attached to the left side of the breaker) was coming out of the bottom of the box, over a fence, thru the door of the shed and tied into the lugs of an old Federal breaker box. It had 8 single pole breakers in it. 2 of those breakers (not adjacent, but at least on different busses) was feeding a 10/3 wire to a 220v dryer plug. Not sure how many amps the dryer was pulling, but suprised the 14awg extentions below survived.
Problem 3. The white wire from the house (if it's neutral) is bonded to ground here and shouldn't be.
Problem 4. The green/red wires and a hot from the right side of the breaker goes down to another 30 amp breaker, which feeds a 30amp RV receptacle. The green and red are the ground and neutrual and they shouldn't be bonded either.

I'm sure were many other problems. I was testing the dryer in order to sell it and noticed one of the breakers in the federal box was off. Flipped it on an the dryer started making a very loud electrical buzz then shut off. The 30am breaker inside the house tripped. No wonder that breaker was OFF!


Needless to say, immediately shut off this breaker below and the 30amp breaker in the house that feeds it.





1630511449462.png
 
  • Like
Reactions: pc1966
Let me explain what we're seeing here.

This is an enclosure mounted on a post near the driveway. The source wire coming up from the black pipe is fed from a 30amp double pole breaker in the house panel. Not sure if the white wire coming from the house is neutral or ground. The wire does appear to be 10/2 at least. The run is probably about 70 feet long.

I've not figured out yet where the wires in from the pipe on the right go yet. I believe they went to the nearby shed, but can't locate them in there.

Problem 1: The red wire, I guess, wasn't long enough, so they extended it with a piece of 14awg!
Problem 2: The 14/2 romex (the loose side was attached to the left side of the breaker) was coming out of the bottom of the box, over a fence, thru the door of the shed and tied into the lugs of an old Federal breaker box. It had 8 single pole breakers in it. 2 of those breakers (not adjacent, but at least on different busses) was feeding a 10/3 wire to a 220v dryer plug. Not sure how many amps the dryer was pulling, but suprised the 14awg extentions below survived.
Problem 3. The white wire from the house (if it's neutral) is bonded to ground here and shouldn't be.
Problem 4. The green/red wires and a hot from the right side of the breaker goes down to another 30 amp breaker, which feeds a 30amp RV receptacle. The green and red are the ground and neutrual and they shouldn't be bonded either.

I'm sure were many other problems. I was testing the dryer in order to sell it and noticed one of the breakers in the federal box was off. Flipped it on an the dryer started making a very loud electrical buzz then shut off. The 30am breaker inside the house tripped. No wonder that breaker was OFF!


Needless to say, immediately shut off this breaker below and the 30amp breaker in the house that feeds it.





View attachment 89498

That looks horrendous!
 
Well done on the little house on the river
Have you told the boys on the river bank. Lol.
1630521840508.png
 
  • Like
Reactions: stevethesparks
I had meant this to be under the dodgy pics thread. Messed up and created a new thread. Lol
 
  • Like
Reactions: DPG
I've never seen 2 conduits sharing the same knockout before, or conduits going so far into an enclosure like that. Quite perverse really.
 
  • Like
Reactions: pc1966 and DPG
Let me explain what we're seeing here.

This is an enclosure mounted on a post near the driveway. The source wire coming up from the black pipe is fed from a 30amp double pole breaker in the house panel. Not sure if the white wire coming from the house is neutral or ground. The wire does appear to be 10/2 at least. The run is probably about 70 feet long.

I've not figured out yet where the wires in from the pipe on the right go yet. I believe they went to the nearby shed, but can't locate them in there.

Problem 1: The red wire, I guess, wasn't long enough, so they extended it with a piece of 14awg!
Problem 2: The 14/2 romex (the loose side was attached to the left side of the breaker) was coming out of the bottom of the box, over a fence, thru the door of the shed and tied into the lugs of an old Federal breaker box. It had 8 single pole breakers in it. 2 of those breakers (not adjacent, but at least on different busses) was feeding a 10/3 wire to a 220v dryer plug. Not sure how many amps the dryer was pulling, but suprised the 14awg extentions below survived.
Problem 3. The white wire from the house (if it's neutral) is bonded to ground here and shouldn't be.
Problem 4. The green/red wires and a hot from the right side of the breaker goes down to another 30 amp breaker, which feeds a 30amp RV receptacle. The green and red are the ground and neutrual and they shouldn't be bonded either.

I'm sure were many other problems. I was testing the dryer in order to sell it and noticed one of the breakers in the federal box was off. Flipped it on an the dryer started making a very loud electrical buzz then shut off. The 30am breaker inside the house tripped. No wonder that breaker was OFF!


Needless to say, immediately shut off this breaker below and the 30amp breaker in the house that feeds it.





View attachment 89498
That looks very dangerous and if it was me I would tear it all out and do it right using the right color wire
 
  • Agree
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dallas
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)