Let me explain what we're seeing here.

This is an enclosure mounted on a post near the driveway. The source wire coming up from the black pipe is fed from a 30amp double pole breaker in the house panel. Not sure if the white wire coming from the house is neutral or ground. The wire does appear to be 10/2 at least. The run is probably about 70 feet long.

I've not figured out yet where the wires in from the pipe on the right go yet. I believe they went to the nearby shed, but can't locate them in there.

Problem 1: The red wire, I guess, wasn't long enough, so they extended it with a piece of 14awg!
Problem 2: The 14/2 romex (the loose side was attached to the left side of the breaker) was coming out of the bottom of the box, over a fence, thru the door of the shed and tied into the lugs of an old Federal breaker box. It had 8 single pole breakers in it. 2 of those breakers (not adjacent, but at least on different busses) was feeding a 10/3 wire to a 220v dryer plug. Not sure how many amps the dryer was pulling, but suprised the 14awg extentions below survived.
Problem 3. The white wire from the house (if it's neutral) is bonded to ground here and shouldn't be.
Problem 4. The green/red wires and a hot from the right side of the breaker goes down to another 30 amp breaker, which feeds a 30amp RV receptacle. The green and red are the ground and neutrual and they shouldn't be bonded either.

I'm sure were many other problems. I was testing the dryer in order to sell it and noticed one of the breakers in the federal box was off. Flipped it on an the dryer started making a very loud electrical buzz then shut off. The 30am breaker inside the house tripped. No wonder that breaker was OFF!


Needless to say, immediately shut off this breaker below and the 30amp breaker in the house that feeds it.





1630511449462.png
 
Let me explain what we're seeing here.

This is an enclosure mounted on a post near the driveway. The source wire coming up from the black pipe is fed from a 30amp double pole breaker in the house panel. Not sure if the white wire coming from the house is neutral or ground. The wire does appear to be 10/2 at least. The run is probably about 70 feet long.

I've not figured out yet where the wires in from the pipe on the right go yet. I believe they went to the nearby shed, but can't locate them in there.

Problem 1: The red wire, I guess, wasn't long enough, so they extended it with a piece of 14awg!
Problem 2: The 14/2 romex (the loose side was attached to the left side of the breaker) was coming out of the bottom of the box, over a fence, thru the door of the shed and tied into the lugs of an old Federal breaker box. It had 8 single pole breakers in it. 2 of those breakers (not adjacent, but at least on different busses) was feeding a 10/3 wire to a 220v dryer plug. Not sure how many amps the dryer was pulling, but suprised the 14awg extentions below survived.
Problem 3. The white wire from the house (if it's neutral) is bonded to ground here and shouldn't be.
Problem 4. The green/red wires and a hot from the right side of the breaker goes down to another 30 amp breaker, which feeds a 30amp RV receptacle. The green and red are the ground and neutrual and they shouldn't be bonded either.

I'm sure were many other problems. I was testing the dryer in order to sell it and noticed one of the breakers in the federal box was off. Flipped it on an the dryer started making a very loud electrical buzz then shut off. The 30am breaker inside the house tripped. No wonder that breaker was OFF!


Needless to say, immediately shut off this breaker below and the 30amp breaker in the house that feeds it.





View attachment 89498

That looks horrendous!
 
Let me explain what we're seeing here.

This is an enclosure mounted on a post near the driveway. The source wire coming up from the black pipe is fed from a 30amp double pole breaker in the house panel. Not sure if the white wire coming from the house is neutral or ground. The wire does appear to be 10/2 at least. The run is probably about 70 feet long.

I've not figured out yet where the wires in from the pipe on the right go yet. I believe they went to the nearby shed, but can't locate them in there.

Problem 1: The red wire, I guess, wasn't long enough, so they extended it with a piece of 14awg!
Problem 2: The 14/2 romex (the loose side was attached to the left side of the breaker) was coming out of the bottom of the box, over a fence, thru the door of the shed and tied into the lugs of an old Federal breaker box. It had 8 single pole breakers in it. 2 of those breakers (not adjacent, but at least on different busses) was feeding a 10/3 wire to a 220v dryer plug. Not sure how many amps the dryer was pulling, but suprised the 14awg extentions below survived.
Problem 3. The white wire from the house (if it's neutral) is bonded to ground here and shouldn't be.
Problem 4. The green/red wires and a hot from the right side of the breaker goes down to another 30 amp breaker, which feeds a 30amp RV receptacle. The green and red are the ground and neutrual and they shouldn't be bonded either.

I'm sure were many other problems. I was testing the dryer in order to sell it and noticed one of the breakers in the federal box was off. Flipped it on an the dryer started making a very loud electrical buzz then shut off. The 30am breaker inside the house tripped. No wonder that breaker was OFF!


Needless to say, immediately shut off this breaker below and the 30amp breaker in the house that feeds it.





View attachment 89498
That looks very dangerous and if it was me I would tear it all out and do it right using the right color wire
 

Reply to Bought me a lake house and found this. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
380
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
811
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
296
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock