ernest1990

Hi all,

I've recently replaced my 4 inch centrifugal extractor fan fitting in the loft. I was hoping for some advice on if this is wired up corrrectly. The fan itself is working well.

Old fan had timer, new fan doesn't have timer.
Both fans are turned of via the pull switch in the bathroom.

I wired it up to match the old wiring:
  • First image attached is the old fan showing its wiring,
  • Second image is the new fan showing the new wiring,
  • Third image shows the existing switches next to the new fan (left off, right on).

With the old fan, this worked with both switches turned on. With the new fan, when both switches are on, the fan runs constantly. If I turn the left switch off and keep right on, the fans works as expected (on and off using the pull switch in bathroom).

Wanted to check if I'm good to leave this set up how it currently is regarding those left and right switches. It doesn't have any issues in how it functions. I just wasn't sure what that left switch has to do with this new fan / how I've wired this new fan up and why it causes the fan to run when switched on.

Any advice is greatly appreciated.

Thanks,
Andy.
 

Attachments

  • 1.jpg
    1.jpg
    535.8 KB · Views: 95
  • 2.jpg
    2.jpg
    525.1 KB · Views: 73
  • 3.jpg
    3.jpg
    566.1 KB · Views: 78
At a guess, the original installer (whose workmanship suggests was not a professional electrician) tried to comply with the manufacturer's instructions that the fan should be fed via a 3A fuse, and the only way he could think of doing this was to fit one in both the permanent live and the switched live.
Any reason you've started a completely new thread?
Still not convinced this is the correct fan. There's no sign of an adjuster for the overrun timer.
 
Last edited:
At a guess, the original installer (whose workmanship suggests was not a professional electrician) tried to comply with the manufacturer's instructions that the fan should be fed via a 3A fuse, and the only way he could think of doing this was to fit one in both the permanent live and the switched live.
Any reason you've started a completely new thread?
Still not convinced this is the correct fan. There's no sign of an adjuster for the overrun timer.

Hi thanks for your reply. The new fan doesn't have an overrun timer. I purposely went for one without it. Thanks.
 
In that case you have connected it incorrectly. The permanent live should just be terminated to a loose connector block and not connected to the fan.
Why would you not want an overrun timer, especially on an inline fan, where the noise problem should be minimal.
 
In that case you have connected it incorrectly. The permanent live should just be terminated to a loose connector block and not connected to the fan.
Why would you not want an overrun timer, especially on an inline fan, where the noise problem should be minimal.
Thanks. Is this a fire hazard in it's current set up?
 
This is probably a two speed fan, and without seeing the installation instructions, I can't say how it should be wired, but as things are, with the switches on, you are applying power to a stalled motor, which possibly isn't a good idea.
Disconnect the permanent live, as I said.
The other thing that stands out as wrong with the wiring is that, not only has the neutral wire not been identified with blue sleeving as required by the regs, but the black wire has been used as the neutral instead of the grey, which is contrary to convention.
 
  • Like
Reactions: nicebutdim
This is probably a two speed fan, and without seeing the installation instructions, I can't say how it should be wired, but as things are, with the switches on, you are applying power to a stalled motor, which possibly isn't a good idea.
Disconnect the permanent live, as I said.
The other thing that stands out as wrong with the wiring is that, not only has the neutral wire not been identified with blue sleeving as required by the regs, but the black wire has been used as the neutral instead of the grey, which is contrary to convention.

Ok thanks for your help.
 
from post #7.

the black wire has been used as the neutral instead of the grey, which is contrary to convention.

conventionally, i agree with not using the black as N, but if sleeved blue, any colour can be used to comply with regs. just being pedantic. nowt better to do atm. 😊😊😊
 
  • Like
Reactions: nicebutdim
.

conventionally, i agree with not using the black as N, but if sleeved blue, any colour can be used to comply with regs.
I'm well aware of that, but neither of the two remaining wires in use are sleeved, and, in the absence of testing, an electrician would assume neutral is live and live is neutral.
More to the point, the sloppiness of the original work suggests a DIY job.
 
  • Like
Reactions: nicebutdim
I'm well aware of that, but neither of the two remaining wires in use are sleeved, and, in the absence of testing, an electrician would assume neutral is live and live is neutral.
More to the point, the sloppiness of the original work suggests a DIY
agree. RAF.
 
When I tested it the first time after fitting there was power going into both L1 and L2, until I turned off the left switch. Could this have damaged the fan motor? It was working fine after. Thanks.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice on centrifugal extractor fan fitting
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
ernest1990,
Last reply from
ernest1990,
Replies
10
Views
1,924

Advert