- Apr 28, 2024
- 3
- 0
- 1
- India
- Trainee Electrician
Recently I have installed Type 2 Surge Protective Device SPD 20 to 40kA, Type1+2, Phase + Neutral + Earth (2 Pole 275 Volt AC) (Uc-275VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV) after 64A DP MCB at home MDB. The home lode is around 1.75KW. We have 220 VAC main line here.
At the evening of 3rd day after installation, the SPD was exploded. I find that the cartridge of Phase side was damaged and it was totally short with earthing terminal. But cartridge of neutral side was in good condition. There was no sign of lightning nearby. No neighbour was affected with Spikes and surges at that time. I am confused about the reason how the SPD got damaged!
Now I am going to replace the SPD with “Type 2 Surge Protective Device SPD (Phase side: Uc-320VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV Neutral Side: Uc-255VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV). Will it be good?
Thanks.
Thanks.