Recent content by 01laverickd

  1. 0

    RCD disconnection times!

    Yeah, that's how I thought it was but went about explaining it the very long way. Thanks for your time. ?
  2. 0

    RCD disconnection times!

    That question has made me see my fault. I've got it from the rcd trip times. I was using the x1 figures of 300ms. If an rcd was used for fault protection (for example 100ma at rated current would be 300ms trip time)? So if I'm using 30ma RCDs regardless wether it's for fault or additional it...
  3. 0

    RCD disconnection times!

    That answers my question. Perfect thanks for that westward10! Explains it all perfectly. I was just a bit q confused as it says 300ms for RCDs at rated current or 0.2 in TT systems. Is that because its the lesser of the two figures (0.2 and 300ms?) So a TN system is 0.4s but rated current...
  4. 0

    RCD disconnection times!

    Haha! It was more just a simple example, so say I had a zs of 85 ohms, which is obviously too high for fault protection from a bs 60898.. So I'd use the 61008 of a split load board say to protect for fault current. So if I got 250ms trip time for the 61008 at rated current would that be OK...
  5. 0

    RCD disconnection times!

    So if it was 250ms would it pass?
  6. 0

    RCD disconnection times!

    Hi all, just a quick one regarding RCD disconnection times. So for non rcd protected circuits disconnection times of 0.4 / 5 seconds and 0.2 / 1 second for TN + TT final and distribution circuits. RCDs (fire / fault protection) usually 300ms at rcd for rated current. (differs when s type)...
  7. 0

    Commercial garage design

    Yeah I thought that was the case. Havent been down that route yet, it's not until the new year but it's certainly the route I want to go down. If not... Circuits that wouldn't normally have to be rcd protected in a TN system have to be offered fault protection in the way of an rcd, in this...
  8. 0

    Commercial garage design

    Any takers? ??
  9. 0

    TT commercial unit upfront RCD

    In any case the rcd could be changed to a 100ma s type Rcd which would offer diversity to the downstream circuits.
  10. 0

    Commercial garage design

    I'm looking at fitting a commercial garage out. I plan to put a 4 pole 300MA S TYPE rcd as main switch on a 12 way 3 phase board providing I can get the Ra down low enough, should be fine though, otherwise it'll be a 100ma s type. Socket circuits and maybe lighting circuits will go on 30ma DP...
  11. 0

    Loss of PME device

    Just seen, they look a little hefty in size though. The pod point looks to be one unit. Nonetheless if they are working are the a good addition in my eyes..
  12. 0

    Loss of PME device

    I'm just curious as to what everyone thinks of the new device that has been made by pod point for their EV chargers? It basically cuts the supply to the charger in the event of a broken PME. Could we see this device being used at the source of PME installations? I personally think it would be...
  13. 0

    TT Submain and switch fuse

    Yeah that's what I thought. So I think the way I'm going ti do it is the best way, 100ma s type rcd for fault protection and a switch fuse adjacent to it for overcurrent protection. Yeah I'm going to go with the two rods and link them aswell. Cheers!
  14. 0

    TT Submain and switch fuse

    Another question! I'm designing for a TT system, there's going to be one 10 way Rcbo consumer unit for the house, less than 3 metres away from the DNO cutout, I'm going to swap the main switch with a 100ma Stype rcd to provide fault protection ( I'll be fitting a tails clamp inside the CU and...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock