    Low bay led lights tripping

    The measured Eli on the 16 amp is 0.95 according to the results at the board not got up there yet to measure myself Apparently they had 100w fluorescents previously and they had them switched out for these 100w low bay leds
  2. A

    Low bay led lights tripping

    Yes that's along the lines of what I was thinking adding an additional circuit and separate it off from the existing. I believe the zs reading is a limiting factor to increase to a 20a type c but I need to check the reading when I get access They are on plugs so I think thats a good idea to...
  3. A

    Low bay led lights tripping

    Ok ok o_O
  4. A

    Low bay led lights tripping

    The supply cable is 1.5mm2 3 core singles in conduit on the 10 amp 2.5mm2 singles in conduit on 16amp
  5. A

    Low bay led lights tripping

    Hi I've been called to a problem where occasionally on cold start up the led low bay lights trip the breakers. The two set ups are; 1. Mcb ncn hager 10 amp type c feeding 6 x 100w low bays and 1 x 150w low bay. 2. Mcb ncn hager 16 amp type c feeding 14 x 100w low bays I have been told by...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock