  1. B

    use of Henley ?

    yes it is notifiable which i can do through my niceic membership weather i should is another question i have the qualifications and the membership of the club i also have a complete lack of ability and knowledge and have relied for most of my life on the supreme confidence of total ignorance...
  2. B

    use of Henley ?

    you didn't do a 6 year apprenticeship since July 2015 when the 3rd amd came in and that was the relevance of the question i rarely get involved in domestic but are having to add accommodation to an industrial unit.
  3. B

    use of Henley ?

    thanks looks like youve answered this before or arnt big on long conversation
  4. B

    use of Henley ?

    with bs7671 Amd 3 2015 is a henley block considered as switch gear and therefore enclosable in non ferous I know it doesn't switch But an MCB wont cause an issue in the open position i have never seen a melted Henly and its not the same plastic as the old CUs anyway your thoughts ?
  5. B

    sub main to outbuilding

    round the 200 when the night stores kick in im just making the point DNO have difrent ruels to us
  6. B

    sub main to outbuilding

    No my moto is im friendly im polite and im cheep **** but cheep but you cant have everthing in life
  7. B

    sub main to outbuilding

    the first thing to say is that i took the job over and the supply was to come from a closer house BUT that house has a 60A supply a hot tub and a 9.5Kw power shower and it is tenanted, the farm owner has an 80A supply to a barn 200m away. the DNO have quoted 105,000 to put in a new 100A supply...
  8. B

    sub main to outbuilding

    unless you are rural , my farm house is supplied (admittedly concentric cable) 650m from the transformer
  9. B

    sub main to outbuilding

    hi guys new to this so sorry if revisiting old stuff. I need to run a sub main 200M from the service head to a log cabin Super eco all LED etc, so 40A 9Kw max demand if i use the cable calculators i get 185mm cable we all know power networks cover huge distance with 35mm cable on 100A supply...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock