Recent content by Daniel Jones

  1. Daniel Jones

    Bulk Emergency key switch

    Hi All, Looking for some advice, I have been issued a drawing of a large warehouse lighting layout. the drawing shows 72 high bay lights including 29 self contained emergencies. The specification from the manufacture details that the Protective device must be a C16 and a maximum of 3 lights...
  2. Daniel Jones

    Asbestos cables????? Rewire periodic inspection

    I have brought this to the clients attention. Future works could be replacing the consumer unit. As in a poor condition. Mismatched Mcbs and circuit being doubled up in 1 mcb
  3. Daniel Jones

    Asbestos cables????? Rewire periodic inspection

    A specialist company was employed. Who verified it through sample tests.
  4. Daniel Jones

    Asbestos cables????? Rewire periodic inspection

    Experts opinion required. Ask to add some addition fittings to a lighting circuit within a shop. Opened up the consumer unit to access the circuit. And noticed the tails from the service head to the meter and from the meter to the consumer unit look very suspicious. I have experience with...
  5. 20181022_150615.jpg

    20181022_150615.jpg

  6. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    ok, a little confused now. sorry for throwing in the volt drop calculate that hasn't helped to flow. I am trying the establish the minimum circuit protective conductor. i have a 50mm² line conductor with a 25mm² CPC protected by a bs88 125A. i have determined the fault current at the...
  7. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    Sorry guys went off on a bit of a tangent asking about the volt drop. But thank you for your responses. Sorry Strima, we must have posted those replies at the same time. The reason I was asking about the fault current was in all the books you calculate the fault current at the extremity of the...
  8. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    Sorry. Someone shoot me. why do i need to work out the fault current at the end of the final circuit?
  9. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    Thank you Richard, As you are an expert i have another question for you regarding volt drop. I came across a volt drop calculation whilst reading one of the many books i now own. This was a lighting circuits and the equation was Volt drop = mV/A/m × (Ib ∕ 2) × Length with an evenly...
  10. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    This forum has some awesome members. The speed that my questions have been answered is amazing. Following on from the cpc sizing when the ocpd is a mcb. I now have a situation where I have a 16A fuse to bs88 with a fault current of over 700A all the manufactures chart only go down to 0.01 so...
  11. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    Thank you, That makes everything crystal clearer. still have a problem with the logarithmic scale for schneider. I have downloaded the brochure. but there are 4 charts for the IC60H 2 on page 335 and 2 on page 338. i have assumed i am to use the one with the A2s but what are the others...
  12. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    lol. I thought i might have been a big ask, only just recovered from last weekend myself.
  13. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    Ok, so been reading all week and still can’t get my head around this. can someone please confirm my thinking on this. Sizing of CPC with an MCB where the disconnection time is less than 0.1 sec. When the disconnection times for an MCB is less than 0.1 sec (instantaneous) you can no longer use...
  14. Daniel Jones

    2396 style question, 2400, short circuit, RCBO,

    35000 is the I2t (let through energy) from the Beama guide to low voltage switches for a BS60898

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock